Slow PLC comm tag settings

Scan time is the rate the OPC driver is polling the device.

Timeout is how long you have till it says it's bad.

Certain conditions can cause it to get a bad read from overloading the comms on the PLC side but I don't think you'll be able to cause that problem over a radio network. It's a thing that can happen but I don't think it's your problem.

I would recommend setting up a longer polling rate on your tag groups. You configure tag groups by clicking the drop down in the tag browser and selecting "Edit Tag Groups". This lets you make a custom tag group that polls slower. Then you can mass edit tags to assign them to the slow polling group.