Your help documentation indicates the PLC5 driver will work with the 1756-ENET module. Will it work with the 1756-ENBT which is far more common? I am having trouble getting this to work with a passthrough to DH+. Maybe its because its not supported?
The PLC-5 driver works with the 1756-ENBT and routing through a DHRIO module to DH+. The connection path will look like 1,6,3,60.
Where:
1 designates the backplane.
6 is the slot of the DHRIO module.
3 is the channel on the DHRIO module. (2 = channel A and 3 = channel B)
60 is the DH+ node of the PLC5. This is in octal.
What is your path architecture?
Ok, I tried this the other day. For host name I put in the address of the CTRLGX gateway. (Help documentation doesn’t reference this for CTLGX passthrough) and for the connect string I used the same as what you stated. What am I missing?
So I have a better understanding, what is the IP Address of the ENBT module, what slot is the DHRIO module in and DH+ Node Address of the PLC?
Can you drill down to the PLC-5 using Linx? It should look something like:
-192.168.1.228, 1756-A7
[color=#FFFFFF][/color]-Backplane, 1756-A7
[color=#FFFFFF][/color]+00, 1756-L1 LOGIX5550, ControlLX
[color=#FFFFFF][/color]+01, 1756-ENET
[color=#FFFFFF]___[/color]02, 1756-ENBT
[color=#FFFFFF][/color]- 06, 1756-DHRIO
[color=#FFFFFF][/color]+CH A, Data Highway Plus
[color=#FFFFFF][/color]-CH B, Data Highway plus
[color=#FFFFFF][/color]02, 1756-DHRIO
[color=#FFFFFF]____[/color]60, PLC-5/20E, FUNCTEST
I don’t think we are on the same page. The 1756-ENBT is a stand alone. (No logix processor). It is used as a gateway. (similar to the old pyramid integrators). This is a very common setup in our plant. The connect string is as follows:
10.24.6.60 = 00, 1756-ENBT/A
- Backplane = 1756-A7/A
+ 02 = 1756-DHRIO/C
- 03 = 1756-DHRIO/C
- CHA = Datahighway Plus
11 = PLC-5/80B
So if you wanted to connect to ZL03_P51, your connection string would be 1,3,2,3
Yea tried that. It just doesn’t work.
The ControlLogix shouldn’t be needed but I’ll test it in-house just to make sure and get back to you.
I tested without the ControlLogix processor through a ENET and ENBT and both connected and browsed fine.
At this point, do the following to create a log file:
- In the Configure section of the Ignition Gateway, select Console.
- Select Levels tab then type in PLC5 and click the Set button.
- Select “Trace” for the level of the xopc.drivers.allenbradley.PLC5EthernetDriver and ABPLC5ConnectRequest items.
- Add a PLC 5 device.
- Email me all the wrapper.log files to support@inductiveautomation.com.
Thank you,
Tom
Files have been sent. Are you using the 1756-ENBT ip address for "hostname? That is what I am using.
Any progress on this?
Sorry for the slow response on this issue.
Question: How many data files is the PLC 5/80 B at station 11 configured for?
I looked at your log files and did some testing and the only thing I found was when I tested with a large number of data files (999) and the browse timed out. If you have a large number of data files, try increasing the Browse Timeout to say 60000 in the device configuration for the PLC 5/80 B. It will also take awhile to collect the browse data in this situation.
I still get the following error(s) when set at 60000 for browse timeout. I am using 10.24.6.60 in the hostname box and have 1,3,2,11 for connect string. See pic above.
ERROR [PLC5EthernetDriver ] [13:04:38,203]: [L11Batchoff] Invalid DHRIO module channel number in path - 1,3,2,11.
INFO | jvm 1 | 2010/02/09 13:04:38 | ERROR [AbstractEthernetDriver$SelectionManager] [13:04:38,203]: Error during NIO selection.
INFO | jvm 1 | 2010/02/09 13:04:38 | java.lang.NullPointerException
INFO | jvm 1 | 2010/02/09 13:04:38 | at com.inductiveautomation.xopc.drivers.allenbradley.requests.ABPLC5ConnectRequest.<init>(ABPLC5ConnectRequest.java:34)
INFO | jvm 1 | 2010/02/09 13:04:38 | at com.inductiveautomation.xopc.drivers.allenbradley.PLC5EthernetDriver.createConnectRequests(PLC5EthernetDriver.java:110)
INFO | jvm 1 | 2010/02/09 13:04:38 | at com.inductiveautomation.xopc.driver.api.AbstractEthernetDriver.channelConnectDone(AbstractEthernetDriver.java:165)
INFO | jvm 1 | 2010/02/09 13:04:38 | at com.inductiveautomation.xopc.driver.api.AbstractEthernetDriver$SelectionManager.run(AbstractEthernetDriver.java:512)
INFO | jvm 1 | 2010/02/09 13:04:38 | at java.lang.Thread.run(Unknown Source)
Anything new on this?