Similiar to the thread linked, I am unable to connect to a Compactlogix processor with my Ignition gateway (v7.9.9).
I can ping the compactlogix from the server with no issues, and I can get online with and program the PLC with no issues.
Typically we use 9300-ENA as our NAT devices, but as the 1783 is considerably cheaper, and takes up less panel space, I am trying a POC to use this router instead.
I’ve tried editing the custom rules on the PLC connection. I’ve opened up tcp/udp port 44818, tcp port 49320, but this does not seem to have any effect.
I’ve added the device on the gateway, and if I add an “IsConnected” tag, it will show True for about 10 seconds, and then go to bad quality.
Been using one of these for a number of years with a CompactLogix L33R v24 on a DLR. Can you show how your Public and Private networks are configured? There is nothing special required on the Ignition side.
I figured out the problem. It had been a long day at the office when I went to setup the device in Ignition. Instead of using the IP address of the PLC, I used the NATR public port address, which was just off by 1 from the PLC. It was throwing me, because the “IsConnected” device diagnostic tag was showing True. I guess the NATR is just enough like a PLC from Ignition’s perspective that it was able to fool Ignition on some level.
Anyway, after posting the question I went back and double checked my settings and realized my mistake. As you’d expect, it’s working perfectly now.