Hey guys,
I’m having some issues with alarms that are set for “Above Setpoint” activating below the setpiont and then never resetting. These alarms have a few differences from other alarms that I have set up so I’m not sure which of them may be causing the issue.
Difference #1: These alarms are on tags that have linear scaling
Difference #2: These alarms have setpoints that are bound to memory tag values
You can see from the pictures below that the alarms are activating when they shouldn’t and resetting hours from when the alarms activate (If you look at the alarm trend it looks like it’s almost working backwards but not respecting the alarm setpoint at all). I kind of have a feeling it might have something to do with the tag having scaling on it, but I’m not sure. FYI.