A button appears to be passing the wrong parameter
When I click on this button:
That should be passing these parameters (Note the hard coded BMS 1):
It populates this table with banks 3&4:
If I go to the designer and input BMS 1 it populates the correct banks:
To me, that says there is a breakdown between the button and the view it is navigating to. I cannot for the life of me figure out what it is. Can someone tell me what I'm missing?
Edit: Deleted images due to potential concerns
So you have a view with a parameter PLC, and you're passing this as the values for the embedded view's parameters PLC and MB_PLC ?
Check that this original PLC parameter is what you think it is.
edit: Wait, I missed the part about the hardcoded parameter.
What happens if you remove the values from the MB_PLC and PLC parameters in the designer ?
also is it number 1 or string "1"
Yes, as Victor notes, I believe hardcoded parameters passed through the navigation event are strings, but the one you put in the designer is an int. This is likely the issue.
Thanks for your help, this worked!