A result set was generated for update
I have a problem running this query on a query tag it returns "A result set was generated for update", but when I run it as a named query (substituting the parameters for test) it works, the problem isn't the parameters since the test query also shows this error in the query tag. The thing is I need this query in the query tag since it has parameters referencing other tags.
SELECT COUNT(DISTINCT CAST(Fecha AS VARCHAR) + '_' + CAST(Hora AS VARCHAR)) AS TotalHorasMalas
FROM (
    -- Horas malas de Orujos
    SELECT CONVERT(DATE, FechaHora) AS Fecha, DATEPART(hour, FechaHora) AS Hora
    FROM Laboratorio_NIR
    WHERE Orujo_{[.]../Parameters.Line} > 2.8
    AND FechaHora <= CAST('{[~]FinTurnoActual}' AS DATETIME)
    AND FechaHora > CAST('{[~]InicioTurnoActual}' AS DATETIME)
    UNION ALL
    -- Horas malas de Sólidos
    FROM Laboratorio_Solidos
    WHERE (Porcentaje_C1 > 0.2
        OR Porcentaje_C2 > 0.2
        OR Porcentaje_C3 > 0.2
        OR Porcentaje_C4 > 0.2
        OR Porcentaje_C5 > 0.2
        OR Porcentaje_C6 > 0.2
        OR Porcentaje_C7 > 0.2
        OR Porcentaje_C8 > 0.2)
    UNION ALL
    -- Horas malas de Acidez
    FROM Laboratorio_FFA
    WHERE (FFA_C1 > 5
        OR FFA_C2 > 5
        OR FFA_C3 > 5
        OR FFA_C4 > 5
        OR FFA_C5 > 5
        OR FFA_C6 > 5
        OR FFA_C7 > 5
        OR FFA_C8 > 5)
    UNION ALL
    -- Horas malas de Humedad
    FROM Laboratorio_Humedad
    WHERE (Porcentaje_C1 > 0.3
        OR Porcentaje_C2 > 0.3
        OR Porcentaje_C3 > 0.3
        OR Porcentaje_C4 > 0.3
        OR Porcentaje_C5 > 0.3
        OR Porcentaje_C6 > 0.3
        OR Porcentaje_C7 > 0.3
        OR Porcentaje_C8 > 0.3)
) AS HorasMalas;
What is the "query type" in the query tag? Based on your error, I would suggest you try 'Select' if it isn't set to that already.
Thanks! That actually worked! changed to Select :slight_smile: