I’ve got a system that is running talking with 2 PLC right now and I am adding one more to the gateway. I am running Ignition 8.1.45 with the AB drivers version 6.1.45.
My PLC is AB L71 running version 17.01. The processor is in slot 2 of the rack with the ENBT in slot 1 of the rack.
I have setup the AB Legacy driver with the IP address of the communication card and set the slot number to 2 where the PLC resides. When I save the configuration I see the driver trying to connect but then it changes to Disconnected. Is there anything else I am missing?
I am expecting that something in the info the customer provided me is wrong. As I can’t create a new PLC program with an L71 at version 17. If I drop the processor down to a L61 I can create a new program at version 17. I am waiting for the IT team to give me access to the PLC IP address so I can do an upload and see for myself what is running.
So now I am online with the processor I can see that it is an L61 processor running version 17.3. So I still need to use the AB ControlLogix Legacy Driver. It is in slot 2 and the ENBT is in slot 1 so I don’t think I need to change the driver configuration.
When I go to the Diagnostic and go to log on the gateway I searched my device name and I see nothing in it for the driver I set up. I also filtered by Gateway.OpcConnectionManager but again I see nothing in the log.
When I go to the OPC quick client I can see the device and it is in a state and status of “Connecting” but the connection remains “false”
The OPC Connection Manager loggers would not be helpful. This is a driver. You should search the loggers for "Logix" and turn possibles to DEBUG. Open a support ticket with IA if you need specific guidance.
(IIRC, the legacy drivers do not tag their log entries with the device name--they haven't been touched by IA since before that facility was added to logging infra.)