AB PowerMonitor 1000 - Cannot read data (OPC)

Has anyone successfully read data from an AB PowerMonitor 1000?

I have tried using Ignitions SLC500 OPC-UA driver and manually entering a PowerMonitor data address into the Tags OPC Server and OPC Item Path fields, but no success.

I have created an OPC topic using RSLinx Gateway. I can view the tag values using the RSI OPC Test Client that comes with RSLinx. I have added the RSLinxOPC to the Ignition OPC Connections Servers. I can open Ignitions quick client and brows the address. HOWEVER, when I try to read an address value with Quick Client (F10:2 for example), it say’s:
"Read Completed [RSLinxOPC] [PMEthIP] F10:2
Status: OPERATION_FAILED
Value: NULL
Quality: [OPERATION_FAILED] null "

Any pointers would be greatly appreciated.

Thank you

Interesting. Consider trying Ignition’s Ethernet PLC-5 driver instead.

Thank you for the suggestion Phil. Yes I had tried this as well as trying the MircoLogix setting.

It’s strange that even the RSLinx OPC not working in Ignition either. It is running on an active license in Gateway mode on the Ignition Gateway server.

I think I solved it. I disabled processor browse in the advanced settings section of the AB SLC 5/05 Ethernet Config.
Shall continue some testing and report back.