ACK all from external button
I start using the new alarm system and I need to setup an external ACK all button.
Can you suggest an easy way to acknoledge all alarm with a button script.
thanks
I’m certian there is a more elegant way, but this worked for me. Hope this helps!
#Global Alarm Ack Button - Script
#Rev 1.0, by T. Smith 6/11/13, C: 303.827.1337
#Samuel Engineering, Denver CO
#Rev 1 Note: Original
#Rev 2 Note:
#Test Table (Rem out when not used, delete when test complete)
If the developer places a table on the same screen, named “table”
it will display the same unacked data as the alarm window.
#table = event.source.parent.getComponent(“Table”)
#UnackedAlarms = system.alarm.queryStatus(state=[“ActiveUnacked”])
#table.data = UnackedAlarms.getDataset()
#Define Variables
#Get all Active and Unacked alarms
AlmData = UnackedAlarms.getDataset() #Create dataset of Unacked alarms
#Loop Through all alarms, and acknowledge them one at a time
#Declare variables
idx = 0
#For Loop through list and ack
for r in results:
resultevent = str(Mydata.getValueAt(idx,‘EventId’)) #Get Alarm Event ID
system.alarm.acknowledge([resultevent],"") #Execute Ack
#Execute Associated PLC tags here
#Plc_Alarm_Ack_Tag
There was a typo on the For Loop portion of the code, the corection is below…
#Declare variables
idx = 0
for r in results:
resultevent = str(AlmData.getValueAt(idx,‘EventId’)) #Get Alarm Event ID
Where do you declare the variable [color=#FF0000]results[/color] and [color=#FF0000]MyData[/color] thanks
With slightly less verbosity:
alarmEvents = system.alarm.queryStatus(state=["ActiveUnacked"])
alarmIds = [str(event.getId()) for event in alarmEvents]
system.alarm.acknowledge(alarmIds, "acked all from script")