I want to list alarm events in a report table in 7.7
I’ve found the event data in the database but can’t seem to find where the cleared and acknowledged info is stored?
For me, a frustrating omission is the inability to access the data in the predefined alarm tables.
If I were doing an alarm report in 7.7 I’d make a hidden table on the page and run a script somthing like this, tied to a Date Range component
[code]start = event.source.parent.getComponent(‘Date Range’).startDate
end = event.source.parent.getComponent(‘Date Range’).endDate
cleared = system.alarm.queryJournal(journalName=“Journal”, state=[“ClearUnacked”,“ClearAcked”], startDate = start, endDate = end)
active = system.alarm.queryJournal(journalName=“Journal”, state=[“ActiveUnacked”, “ActiveAcked”], startDate = start, endDate = end)
#dataset to pass to the table
dataset = []
#dataset to check the UUID of each event
checked = []
#Check all active alarms
for alarm in range(len(active)):
id = active[alarm].getId()
#If we have not checked an alarm with this ID...
if id not in checked:
#...add the UUID to checked
checked.append(id)
#get the time the alarm went active and convert it to a string
#also, I clean up whe is returned
activeDate = str(active[alarm].getActiveData())[11:22]
activeTime = str(active[alarm].getActiveData())[22:30]
# ack = active[alarm].getValues()
alarmName = active[alarm].getName()
DP = active[alarm].getDisplayPath()
Priority = active[alarm].getPriority()
State = active[alarm].getState()
#The loop that checks for cleared alarms
for i in range (len(cleared)):
#find the matching cleared event if one exists
if cleared[i].getId() == id:
#format the cleared event time
clearedTime = str(cleared[i].getClearedData())[22:30]
clearedDate = str(cleared[i].getClearedData())[11:22]
#Attempt to add the UUID, active time, and cleared time to the dataset named “dataset”.
try:
dataset.append([DP,alarmName,activeTime,activeDate,clearedTime,clearedDate,Priority,State])
#if the append fails because cleared time is NULL, then insert a NULL into that column of the dataset
except NameError:
dataset.append([DP,alarmName,activeTime,activeDate,None,None,Priority,State])
else:
pass
#Reset clearedTime for the next iteration through the loop
clearedTime = None
header = [“Name”,“Alarm”,“Active Time”,“Active Date”, “Cleared Time”,“Cleared Date”, “Priority”, “State”,]
dataset = system.dataset.toDataSet(header, dataset)
event.source.parent.getComponent(‘Table’).data = dataset[/code]
You will have to modify it a bit to get the info you need, if you want cleared alarms as well, but it gives you something like the Alarm Journal in a table
You can then make the table one of your data sources.
Thanks Chris, had a go at that, got past a few stumbling blocks but it’s reporting on the line:
“alarm not defined”
any tips?
alarm is defined in the line above
spelling and case correct?
Hi Chris, strange, I 1st tried this on my laptop and got that error… I moved onto the desktop and copied the code and it worked 1st time… thanks again for your help