Alarm in Active But Not Logging to Database

We have several hundred alarms configured in the system and I am seeing strange behavior by one that is a alarm monitoring machine state. There are 3 states configured all to equal mode. 0=Down 1=MG Sets Running and 2=Excitation Up.
The alarm triggers as it did in the 7.5 version and it shows up in the new Active Alarm component as expected but it never logs to the database. This is very odd other alarms are pushing to the db as expected. There are no errors in the logs when this happens that I have seen.

Found this one my bad when I initially setup the gateway for the new settings I left the minimum priority at low since that used to be the lowest value. Well now the lowest is Diagnostics so my bad on this one. But maybe this will help some one else if they see the same thing.