I have an issue with Alarm Metrics in Ignition 8.3.
I have a folder with many UDT instances which can trigger alarms. I created a reference tag with reference to “[.]Alarm Metrics.activeAckCount”, however I noticed that the tag as well as the Alarm Metrics tags are not updating unless I open the particular folder in the tag browser.
The reference tag also includes a value change script writing the Alarm Count to a SQL table, which is not updated if the folder is not open in tag browser.
Try with an expression tag instead of a Reference tag. The alarm metrics have a lightweight internal implementation that avoids execution when not subscribed, and a reference tag isn't a subscription. (I think. Might be a bug worth reporting.)
After some time, I noticed that it is not working reliably. After a restart, I have to open all folders where the instances are located to refresh the Expression Tag with activeAckCount.
I changed the execution mode from Event Driven to Tag Group (Default), but nothing changed.
These Alarm Metrics have taken a lot of my time and are only causing issues. It would be better not to include them in the Designer if they are not working as expected.
In the end, I implemented my own alarm metrics system.
To be honest, I thought you were part of the IA team or that someone from IA was reading this forum. I didn’t expect IA to fix this bug for me or update the documentation.
I mainly wrote this to inform other integrators like me about the issue, because over the past few years I’ve found many similar posts here that saved me a lot of time.
If something else is actually subscribed to that set of Alarm Metrics, I would expect a Reference Tag to work. But the Reference Tag itself won’t generate a subscription. Expression Tags would be my approach as well in this use case.
To the other question/issue:
If you’re able to provide more specifics as to your setup and what you’re seeing we’ll be able to help out more.
Anyway, if the value of the reference or expression tag is displayed in a view - isn't this a subscription?!
No. You are simply viewing the value that reference or expression tag evaluates to. An expression tag will create a subscription to the Alarm Metric and keep it alive, a reference tag will not.
Expression tags are working without issue for the exact case you're describing. Here's the tag JSON:
If you're looking for more input, you're going to need to give more detail as to what your setup looks like, what you have configured, and exactly what is not functioning as you'd expect. Everything until now looks as expected from the Ignition side.