The fact that display path is a “path” doesn’t mean a lot right now, but will become more useful when we make components like trees that let you browse down by source or display path. It’s perfectly fine if your display path doesn’t include “/”, it would then technically be a path of only 1 element.
Anyhow, in certainly [del]is[/del] will be possible to do what you want. (big note: Unfortunately as I tried to mock this up in order to verify everything, I found a few problems that would keep this from working in the current beta. They’ve been fixed for the release. So, I’ll describe the procedure, but you’ll have to wait to try it)
Fundamentally, you’re going to bind the display path to an “expression”. The job of this expression is to return a string. For your example (which isn’t 100% clear to me, but I assume is using 3 tags), the easiest way is:
concat({[.]Site_Name}, " ", {[.]PDU_Name}, " ", {[.]MCB_Name})
Now, it seems to me that these parameters aren’t really ever going to change (though I could be wrong). If so, the performance would be better to use UDT Parameters instead. If using only UDT parameters, you don’t need to bind the display path value, you can just type them in directly:
Display path: {Site_Name} {PDU_Name} {MCB_Name}
Note: I’ve used the same names, but remember, these would be defined as parameters on the data type.
If you want to mix udt parameters and tag references, you can do that, but remember that UDT parameters get expanded before the expression is parsed. So if your site name was a tag, but the other two were parameters, the correct syntax would be:
concat({[.]Site_Name}, " {PDU_Name} {MCB_Name}")
So, you see, the references are inside the quotes, because they’ll get replace with the actual values before the expression is parsed. If they were outside the quotes, they would look like non-existent keywords to the system.
Sorry for the inconvenience of not being able to try this out, but at least I can say that it’ll work for the next update/actual release.
Regards,