Alarm on BACnet tag goes active but never enters the notification pipeline (memory tag alarm works)

Hi everyone,

I'm new to Ignition and building an alarm board, and I'd appreciate help with a notification issue.

Setup

  • Ignition 8.1 (trial), Perspective alarm status table
  • Alarm notification pipeline: Splitter → Notification block (email, on-call roster) → Delay → Expression (isAcknowledged) → Script (phone call)
  • Second Splitter output → Notification block emailing a second roster

What works

  • A memory tag (simulated temperature) with an Above Setpoint alarm sends the email correctly through this pipeline.

What doesn't work

  • A BACnet/IP tag (live value from a Niagara JACE, through the Ignition OPC UA server) with an alarm set up the same way goes Active, Unacknowledged on the alarm status table, but no email is sent and nothing appears in the gateway logs.

What I've checked

  • Both alarms use the same Active Pipeline: samplequickstart/management_pipeline
  • Ack Mode is Manual; the alarm is left unacknowledged for 2+ minutes
  • Email profile test works, and the From Address issue (SendAsDenied) is fixed
  • Alarm Notification module is running, and the project is enabled
  • Both rosters have a user with an email address

The only differences in the tag JSON

  • The BACnet tag is readOnly: true
  • Its alarm has empty custom properties left over from earlier (CustomEmailSubject: "", CustomEmailMessage: "", voip.customMessage: ""), plus empty ackPipeline and clearPipeline

Could the empty custom message properties stop the notification, or is there something else that would keep an alarm on an OPC tag from entering the pipeline?

Thank you!

Have you checked the diagnostics log to see if any errors are being reported there?

Thanks for replying! Yes, I checked Status → Diagnostics → Logs and set the logger alarm.Notification.EmailNotificationProfile to TRACE.

  • Memory tag alarm: the logs show it entering the pipeline and sending the email. An earlier SendAsDenied error from the From Address is now fixed, and these emails arrive.
  • BACnet tag alarm: nothing at all is logged for it. No pipeline entry, no notification attempt, no errors. The only entries around that time are the pipeline being retired and restarted when I save the project. Status → Systems → Alarm Pipelines also shows 0 items while the alarm is active and unacknowledged.

Make sure you didn't typo the pipeline. Make sure it's actually in the "Active" section... I've accidentally put it in the wrong one before looked at it multiple times before realizing it. From an alarm standpoint, it doesn't matter the type of tag.. the alarm is just looking at the value property. So there must be something screwed up in your alarm config.

Thank you so much! I finally found the culprit. The notification block script had a default email address set, and strangely, it kept reverting to that same email even after I saved my changes. I ended up stopping Ignition through Task Manager and restarting it, and that fixed the issue!