Tag Alarms set Bit State.
How to set Event Value equal to Bit value ,not to Value?
Can you display the bitPosition in the alarm table? Otherwise, you might need to create an associated data with the bit number in it and display that ![]()
One approach that would work would be to move your associated data expression to the label property:
Then, you could use the method I developed for renaming alarm status table columns to change the column headers in the table:
if event.propertyName == 'componentRunning':
def getTable(statusTable):
for component in statusTable.getComponents():
if component.__class__.__name__ == 'AlarmStatusTable$1':
return component
else:
table = getTable(component)
if table:
return table
table = getTable(event.source)
tableHeader= table.tableHeader
columnModel = table.columnModel
for column in range(table.columnCount):
tableColumn = columnModel.getColumn(column)
if tableColumn.headerValue == 'Label':
tableColumn.setHeaderValue("Real Alarm Value")
elif tableColumn.headerValue == 'Event Value':
tableColumn.setHeaderValue("Tag Value")
tableHeader.repaint()
Result:
This is a good solution.