Allen Bradley ControlLogix v35 Driver - Tags have Bad Quality (Connection issue)

I have a Issue, regarding a earlier fixed problem.

I have issue that after losing connection to the PLC (due to downloading for example) Ignition does not find a way to reconnect itself to the plc.

It works if i disable and enable the device in the gateway, but shouldn't this just reconnect by itself?

Have you turned off the device's autobrowse? Turning this off improves performance overall by ignoring small changes in the PLC, but breaks comms if you make major changes.

Choose.

(If that's not it, you may need support to look at your situation.)

Unfortunately, this was already enabled.

IIRC, there are AB firmware versions that don't reliably report changes on download and/or small changes. You probably need IA support to help you check that.

(My alternate driver deals with this differently, so I haven't paid much attention.)