Allen Bradley Driver Differences
I have built my UDTs around OPC tag paths based on Allen Bradley PLCs that are version v21+ so I’ve been using the Logix driver.
However, I now have one PLC that is lower than v21. Up until now I have been using the same Logix driver for this device connection but I have noticed that the tag connections are much slower so every once in a while the tags will get bad quality and have an overlay but then the tag updates again and it’s fine.
Assuming that the OPC tag paths are different between the drivers and I would not be able to simply use the existing UDT with the older driver, I’m wondering what the OPC tag path differences may be. Is this documented anywhere? And do the OPC tag paths differ between the CompactLogix and ControlLogix legacy drivers?
Or if anyone has a solution to stop the tag from going into bad quality so often that would work too.
Hmm. Maybe?
But the differences can be automated with regex-based search and replace. Controller tags in the legacy format have an extra global. prefix, and all arrays have an extra named layer. (SomeArray.SomeArray[0] instead of just SomeArray[0].)
Same in both ControlLogix and CompactLogix.
Have you tried my alternate driver? (Keeps the v21+ OPC Item Path format and I don't recall significant performance probems.)
Which specific revision of v20? For example, if it is v20.19 performance will be bad with either driver and you probably will want to change the firmware.
I’ve decided to just update the UDTs to include “Legacy_Scope” parameter that appends to the OPC path. It’s an empty string by default
Unless you only have atomic tags, this won't cover all of your needs.
Care to elaborate? In cases where arrays are used I also have a “Legacy_Array” parameter.
I guess idk what constitutes an atomic tag vs a non-atomic tag.
Arrays of UDTs containing array members? Or deeper nested? Keep in mind that the fragment need with arrays is not constant--it has to match the array name. You should spend some time browsing a legacy processor's tags.
{ I'd make separate UDTs for legacy versus modern. }
I’ve tested it with my arrays. I will adjust as needed.
I did, and that’s how I came up with the format
Care to enlighten me on what atomic tags are or what a non-atomic tag would be?
Atomic tags are non-array non-UDT simple tags.
Got it. Yes, those would need to be handled on a case-by-case basis for those individual tags
FWIW anyone who finds this and wants to do the same, make sure you enter a character in the string parameter default value and then remove it otherwise you’ll get “null” instead of ““