Hi All,
In one of my application i would like to communicate B&R Automation X20 PLC (X201583) with Ignition over OPC UA.
I would like to know the Following.
- Whether B&R Automation PLC X201583 is supported by Ignition.?
- If so how to configure the Device? Which Driver shall I use?
- How to configure OPC-UA?
Best Regards
Vikas
[quote=“vikasgodbole”]1. Whether B&R Automation PLC X201583 is supported by Ignition.?[/quote]Not specifically, but it appears you can add a BC0087 module to add Modbus/TCP to your system.
[quote=“vikasgodbole”]2. If so how to configure the Device?..[/quote]That would be in the BC0087 Manual
[quote=“vikasgodbole”]…Which Driver shall I use?[/quote]The Modbus/TCP Driver
[quote=“vikasgodbole”]3. How to configure OPC-UA?[/quote]Here is the section on the Modbus/TCP Driver in the Ignition user manual.
Hi Jordan,
Thank you so much for your reply.
It would be great help if you clarify the following queries.
Where can i get the BC0087 manual.?
How to add BC0087 module in Ignition?
Best Regards
Vikas
Hi Jordan,
What ever query i wrote in my earlier reply i got the answers for thouse queries.
Where can i get the BC0087 manual.? - BC0087 is B&R Module manual.
How to add BC0087 module in Ignition? - I have to add this module in B&R system.
I am using the available Ethernet port of X201583 to connect B&R X20 PLC to Ignition over OPC-UA.
Is is possible to connect B&R PLC X201583 to Ignition without using BC0087 module?
Steps followed to connect the B&R PLC and Ignition without using BC0087 module are as follows.
- B&R PLC (Available Ethernet Port) --------->(Cat 5) Cable ---------> Ignition PC
- I created the “New Device” clicking “Add New Device”
- I configured the B&R PLC’s IP address and Port number in the “Newly Created Device”.
- Clicked on “Save”
- Ignition shows status of Device as “Connected”
- I configured the IPAdrees, Subnet mask manually in PC(Network Connection >Local Area Connection>Properties > TCP/IP ) on which Iginition is installed.
- In Ignition i clicked on “Add OPC Server configuration”
- I configured HostName: localhost , Port: 4096
- Clicked on “Save”
- OPC-UA Server was running successfully.
- I can Browse B&R PLC in the Ignition but unable to see Tags which i created as Global Tags in B&R PLC.
Kindly suggest.
Best Regards
Vikas
In order to integrate B&R you can:
1.-Use Modbus.
2.-Buy the B&R PVI OPC DA licence (HW key).
3.-Buy the B&R OPC UA licence, I’ve not experience with this one,in fact I’m not sure they have already launched it.