BACnet Driver not connecting to units - database-revision property

Hi kyler.kamyszek,

Thank you for opening a support ticket to get your issue addressed.
In case if others run into similar issues, Kyler and I were able to find that there was a duplicated net stat process causing the BACnet devices to not initialize to the Ignition server. You can check the processes on port 47808 (This is the default bind port for the local device connection) by running netstat -anon | findstr "47808" in a elevated command prompt. If you have a singular local device connection, there should only be a single UDP process listed. When there are duplicated processes this will result in the BACnet devices to not initialize with the Ignition local device. To resolve this, you will want to restart the Ignition Gateway to remove the duplicated process.