BACNET Schedule Object
Hello All,
I’m trying to connect Bacnet Schedule with native Barnet driver, unfortunately it seems
that this type is not recognized.
Extract of objects enable in our device :
Extract of tag recognised by driver :
but no trace object name “OccupancySchedule”.
are there plans to integrate it in a future version?
best reagards
Hi Kevin,
I saw in your first post that recognised objects were :
The set of BACnet Objects currently supported are:
  • Device
  • Analog Input
  • Analog Output
  • Analog Value
  • Large Analog Value
  • Binary Input
  • Binary Output
  • Binary Value
  • Multi-State Input
  • Multi-State Output
  • Multi-State Value
I thought that schedule object was integrated quickly cause it is one of the most important object in the BMS.
Is it planned?
best
Just to push the post to @Kevin.Herron
me2 @Kevin.Herron; back in 2013, I’ve quoted BACnet scheduler as an example for generic calendar management Alarm Module - Schedule
It’s “planned” but there is no timeline assigned to it.
Following up on this a few months later. Any change to priority on getting the Schedule Object released, @Kevin.Herron ?
Cheers!
Oscar.
No, sorry, nothing has changed yet.
Hello, I attach to this chat. I'm evaluating the product, section of it will be related to BACNet BMS systems. I cannot find BacNet/Secure protocol suppport but also I cannot find the management (driver + HMI object representing it) for BacNet schedule object. This post is 4-years old. Has been this fundamental support for a normal BMS application released? Many thanks, Davide
I think the schedule object can be interacted with via readRaw and writeRaw scripting functions, but it’s more of a workaround.
No support for BACnet/SC.
Tks, Kevin. For a BMS application this missing support (BACNET/SC is useful also for NIS2 in Europe) and the missing native management of schedule objects are a big lack, in my opinion. Do you know if they are scheduled ? I understand first requests are from 2021
We’re aware of these requests from a product management standpoint but they are not scheduled or on the roadmap right now.
I have used the equipment schedule and scripting to create a functioning BACnet schedulel. I will share the details