Boolean values from modicon OPC UA PLC are logged in historian core strangely
Howdy,
Boolean values in my historian are not being recorded as true or false, instead the tag history just counts up or down forever, I see the same behavior with a memory tag or a OPC tag from my PLC.
I am using ignition maker edition 8.3 and historian core, so I don’t know if this is the normal behavior of historised boolean values, but I was expecting them to just be recorded a 0 or 1. Here is an example power trend of 2 boolean values (heat is currently on, cool is off).
And the associated tag configuration:
Do they come as Booleans in the Tag Browser?
Yes, If I browse and add tags directly from the OPC server they are automatically added as booleans.
Welcome!
Some further insight for you:
That’s an interesting read! I did already set all my boolean tags to discrete style deadband that are set to “on change” recording. I might also change my process variable to discrete now, to get the more predicatable behavior.
Here are some more examples of trends for my same boolean tag:
I don’t know if you can use Embr Charts on Maker, but if you can, then you should.
I was able to import the Embr Charts module, looks like it’s free for anyone to use!
All,
I was able to fix this manually by changing the pen setup in my powerchart for boolean tags, specifically setting aggregateMode = "LastValue".
since I didn’t want to do do that everytime I added a new tag I applied this on change scipt to the props.pens attribute:
def valueChanged(self, previousValue, currentValue, origin, missedEvents):
    # Iterate through all pens currently on the chart
    pens = self.props.pens
    for i in range(len(pens)):
        try:
            # 1. Get the Source Path safely
            # Structure based on your JSON: pen -> data -> source
            pen_data = pens[i].get("data", {})
            source_path = pen_data.get("source", "")
            # 2. Check if valid tag path
            if source_path and "tag:" in str(source_path):
                tag_path = str(source_path).split("tag:")[-1]
                # 3. Check Tag Type
                configs = system.tag.getConfiguration(tag_path, False)
                # 4. Apply Logic for Boolean Tags
                if configs and str(configs[0].get("dataType")) == "Boolean":
                    # Fix Interpolation: 'display' -> 'interpolation' = 'curveStep'
                    if pens[i].display.interpolation != "curveStep":
                        self.props.pens[i].display.interpolation = "curveStep"
                    # Fix Aggregation: 'data' -> 'aggregateMode' = 'LastValue'
                    if pens[i].data.aggregateMode != "LastValue":
                        self.props.pens[i].data.aggregateMode = "LastValue"
        except Exception as e:
            # Ignores initialization errors (e.g. when a pen is created but not yet populated)
            pass