[Bug-14862,14780]Tag needs restarting after change to tag parameters

ignition80
#1

Whenever we make changes to parameters on a tag parameter the tag needs to be restarted in order for alarms to updated.

In our alarm display path we are referencing an ‘AlarmPrefix’ Parameter on the tag.
If we make a change to this parameter then the tag needs to be restarted in order for the alarms to be updated.

Another issue we are having is the we are putting a ‘BuildingName’ string at the front of the displaypaths which is being read from a tag. When we change any UDT configured alarm properties this tag is not being pulled into the displaypath unless we restart each instance of that UDT.

Version 8.0.4 nightly

0 Likes

#2

These are both issues we are aware of. We appreciate you confirming that we are aware of the problems. The issues are currently being prioritized so there isn’t an ETA on resolution.

Garth