OPC-UA moule in Faulted state after upgrade.
Reported Exception:
java.lang.IllegalArgumentException: Invalid UUID string:
Platform: Windows10
Ignition version: 8.0.0-beta0 (b2018110602)
Java version: 11.0.1
Reported Exception:
Platform: Windows10
Can you upload the wrapper log? We need the full trace for the exception to help debug the issue.
This might be tricky because Windows will hide this file by default, but in the $INSTALL/data/opcua directory there should be a .uuid file… try deleting this and restarting the gateway? From the error message it looks like somehow it exists but is empty.
@Kevin.Herron
Yes, that worked. After the restart the OPC connection to the Ignition OPC-UA server was failing with the following exception (I managed to get it working again by setting the connection endpoint again):
UaException: status=Bad_CertificateUriInvalid, message=The URI specified in the ApplicationDescription does not match the URI in the Certificate.
at org.eclipse.milo.opcua.stack.core.util.CertificateValidationUtil.validateApplicationUri(CertificateValidationUtil.java:222)
at com.inductiveautomation.ignition.gateway.opcua.client.ClientManager.initializeObject(ClientManager.kt:107)
at com.inductiveautomation.ignition.gateway.opcua.client.ClientManager$initializeObject$1.invokeSuspend(ClientManager.kt)
at kotlin.coroutines.jvm.internal.BaseContinuationImpl.resumeWith(ContinuationImpl.kt:32)
at kotlinx.coroutines.DispatchedTask$DefaultImpls.run(Dispatched.kt:235)
at kotlinx.coroutines.AbstractContinuation.run(AbstractContinuation.kt:19)
Azul Systems, Inc. 11.0.1
This was fixed on the nightly uploaded on 11/7