Can not connect to DH485
Can someone help me connect to a PLC SLC 5/02 Processor through an IP address and a DHRIO card then DH485
This is for a OPC/UA topic
You'll need to use connection paths in your device connection to talk over the DH485 card. The example in the docs is specifically SLC over DH+, conveniently!
Using that guide, looks like your connection path should be 1,2,2,8.
As far as I know, Ignition follows all the same rules as CIP routing in Logix.
Thank you, I Did try that 1,2,2,8 from the video. This is DH485 I believe and not Plus if that matters this is what it says
I checked on Rockwell's Knowledgebase (Answer ID BF5708 - TechConnect required). Both DHRIO and DH-485 use 2 for Channel A and 3 for Channel B.
Out of curiosity, can you connect to any other PLCs on either the DH+/DHRIO bus?
I did just notice this though, this is probably your issue:
Supported SLC Connection Methods
  • SLC505 direct
  • SLC505, SLC504, SLC503 connected through 1761-NET-ENI
  • SLC504 connected through 1756-DHRIO
  • SLC505, SLC504, SLC503 connected through Spectrum Controls WebPort 500
No mention of the 1756-DH485 card you're using. Or SLC 501/502 at all, for that matter.
Thank you for taking the time to reply, yes the ones highlighted I am able to connect and read tags. I just cannot connect to the circled PLC.
Right, the highlighted ones are ethernet and DH+. Ignition's docs don't show any support for DH485.