Cannot browse connection "Ignition OPC-UA server"
I am running Ignition 7.8.2 on
“Linux CCDebianCF 3.20-4-686-pae #1 SMP Debian 3.2.68-1+deb7u3 i686 GNU/Linux”
Simulator Devices:https://ge.box.com/s/mbf895g29qflwn498o8adcth6gzlwile
OPC UA setting https://ge.box.com/s/by1fcptvo44fep4kp6qhsowg6qewjoe3
OPC server connection https://ge.box.com/s/r4fk5ff4eurgp5kphgpuxj0wexasu87x
Endpoint https://ge.box.com/s/z5uz9gwm17gkw842vtvlutffrr5n1i7r
Error message: https://ge.box.com/s/zafsv82duq31alo1kpt03e1xftgx4ak7
License: https://ge.box.com/s/gwcw5gf3vplpxsenmx0fkw2ct0ajjgpb
Is there anything missing during my configuration? I had tried to restart the gateway or OPC-UA module.
Thanks. Hope the image links above work or please refer the attachment.
Yongzhi
Under the server settings, the “Endpoint Address” setting should just be the IP address of the machine you’re on. After setting it you’ll need to restart the gateway.
Thanks for the advice. The problem is still there.
OPC-UA > Settings > Server > Endpoint Address > changed to “opc.tcp://3.242.222.148”
OPC Connections > Servers > created a new name and description, authentication “opcuauser/password”
OPC Connections > Servers > OPC Server Connections > endpoint > Discover OPC-UA Endpoints > “opc.tcp//3.242.222.148:4096”, check “opc.tcp//192.168.1.21:4096/iaopcua/None”
OPC-UA module restarted,
Gateway restarted.
It is solved. There is a hidden router somewhere in my machine. The solution is
1.OPC-UA -> Settings -> Server -> Endpoint Address -> 3.222.123.456 (IP address of my machine)
2. OPC Connections -> OPC Server Connections -> endpoint -> Discover OPC-UA Endpoint -> opc.tcp://3.222.123.456:4096
Thanks all and Sam Ngeru.