Cannot run prepared statement while gateway is in disconnect

Hi,

When I try to run any update sentence for SQL Server in preview mode from FactoryPMI Designer, appears me the next error:
“Cannot run prepared statement while gateway is in disconnected or read-only mode”

Any idea?

Thanks

Either your designer is disconnected from the gateway or you are in read-only mode :stuck_out_tongue:

This is the user manual entry for Ignition on communication modes, but the same applies to legacy FPMI.

You need to switch the communication mode to Read/Write before you can run update queries.