Catching a tag write timeout exception
Hello,
I’ve been troubleshooting the following error:
java.util.concurrent.TimeoutException: null
at java.base/java.util.concurrent.CompletableFuture.timedGet(Unknown Source)
at java.base/java.util.concurrent.CompletableFuture.get(Unknown Source)
at com.inductiveautomation.ignition.gateway.script.GatewayTagUtilities.writeBlockingImpl(GatewayTagUtilities.java:261)
at com.inductiveautomation.ignition.common.script.builtin.AbstractTagUtilities.writeBlocking(AbstractTagUtilities.java:482)
at jdk.internal.reflect.GeneratedMethodAccessor55.invoke(Unknown Source)
at org.python.core.PyReflectedFunction.__call__(PyReflectedFunction.java:190)
at com.inductiveautomation.ignition.common.script.ScriptManager$ReflectedInstanceFunction.__call__(ScriptManager.java:540)
at org.python.core.PyObject.__call__(PyObject.java:494)
at org.python.core.PyObject.__call__(PyObject.java:498)
at org.python.pycode._pyx177310.pullOperatorLoadTimeFromPLC$6(:334)
at org.python.pycode._pyx177310.call_function()
at org.python.core.PyTableCode.call(PyTableCode.java:173)
at org.python.core.PyBaseCode.call(PyBaseCode.java:168)
at org.python.core.PyFunction.__call__(PyFunction.java:437)
at org.python.pycode._pyx177304.threadType1$2(:189)
at org.python.pycode._pyx177304.call_function()
at org.python.core.PyBaseCode.call(PyBaseCode.java:306)
at org.python.core.PyFunction.function___call__(PyFunction.java:474)
at org.python.core.PyFunction.__call__(PyFunction.java:469)
at org.python.core.PyFunction.__call__(PyFunction.java:464)
at org.python.core.PyObject._callextra(PyObject.java:589)
at org.python.pycode._pyx177305.run$3(:15)
at org.python.pycode._pyx177305.call_function()
at org.python.core.PyBaseCode.call(PyBaseCode.java:197)
at org.python.core.PyFunction.__call__(PyFunction.java:485)
at org.python.core.PyMethod.instancemethod___call__(PyMethod.java:237)
at org.python.core.PyMethod.__call__(PyMethod.java:228)
at org.python.core.PyMethod.__call__(PyMethod.java:218)
at org.python.core.PyMethod.__call__(PyMethod.java:213)
at org.python.core.PyObject._jcallexc(PyObject.java:3565)
at org.python.core.PyObject._jcall(PyObject.java:3598)
at org.python.proxies.utils$JythonRunnable$33.run(Unknown Source)
I understand that this is occurring because my writes are failing to complete within the timeout. I was originally not using the optional timeout parameter, but now I am, although I have it set to 45000ms, which is the same as the default. There is no reason my writes should take more than 5 seconds to complete, 45 seconds should be plenty.
So that leads me to my next issue, I am trying to catch the error so I can pass in some parameters to the fault message to help me diagnose which PLC it is failing on, so I can investigate for connection issues. I am using a try/except clause around my writeBlocking calls but I am still getting unhandled exceptions.
The code for the above error message looks as such:
def pullOperatorLoadTimeFromPLC(plant, deviceName, opName):
	logger = system.util.getLogger("Project6.prod_record.pullOperatorLoadTimeFromPLC")
	UDTPath = '[Project6]Plant %s/%s/%s/' % (plant, deviceName, opName)
	paths = [
	UDTPath+'OPC/Operator Load Time/Time/Time_8_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_8_/ReadyToGrab',
	UDTPath+'OPC/Operator Load Time/Time/Time_7_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_7_/ReadyToGrab',
	UDTPath+'OPC/Operator Load Time/Time/Time_6_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_6_/ReadyToGrab',
	UDTPath+'OPC/Operator Load Time/Time/Time_5_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_5_/ReadyToGrab',
	UDTPath+'OPC/Operator Load Time/Time/Time_4_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_4_/ReadyToGrab',
	UDTPath+'OPC/Operator Load Time/Time/Time_3_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_3_/ReadyToGrab',
	UDTPath+'OPC/Operator Load Time/Time/Time_2_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_2_/ReadyToGrab',
	UDTPath+'OPC/Operator Load Time/Time/Time_1_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_1_/ReadyToGrab',
	UDTPath+'OPC/Operator Load Time/Time/Time_0_/LoadTime',
	UDTPath+'OPC/Operator Load Time/Time/Time_0_/ReadyToGrab',
	values = system.tag.readBlocking(paths)
	#Mass write all values back to zero immediately after reading.
	try:
		system.tag.writeBlocking(paths, [0,False,0,False,0,False,0,False,0,False,0,False,0,False,0,False,0,False], writeTimeout)
	except:
		logger.warn("Failed to write zeroes to operator load time opc tags for plant %s %s %s" % (plant, deviceName, opName))
	#Get current target load time:
	try:
		targetLoadTime = get.getOperatorLoadTimeOPC(plant, deviceName, opName)
	except:
		targetLoadTime = 0
		logger.warn("Failed to get target load time for plant %s %s %s" % (plant, deviceName, opName))
	#Start sql insert
	for value in values:
		if isinstance(value.value,float):
			loadTime = value.value
			if loadTime>0:
				currentTime = get.getOpCurrentLocalTime(plant, deviceName, opName).replace(tzinfo=None)
				params ={
				'table':'P'+str(plant)+'_pd_operator_load_time',
				'deviceName': deviceName,
				'opName': opName,
				'operatorLoadTime':loadTime,
				'date_time':currentTime,
				'targetLoadTime':targetLoadTime,
				try:
					system.db.runNamedQuery("Project6","Operator Load Time/insertOperatorLoadTime", params)
				except:
					try:
						system.db.runNamedQuery("Operator Load Time/insertOperatorLoadTime", params)
					except:
						logger.fatal("Failed to run sql query for plant %s %s %s" % (plant, deviceName, opName))
						return
		else:
			pass
Does anyone have any ideas on what I can do to properly catch this error?
Generally speaking try/except will only catch python errors. To catch java errors in Ignition, you have to import them, for instance to catch an error that the database throws you would need
import java.lang.Exception
try:
   system.db.runUpdateQuery("somequery")
except Exception, e:
## catches python errors
except java.lang.Exception, e:
## Catches database thrown errors
Looking at your stack trace it looks like ultimately you get java.util.concurrent.TimeoutException so that is the exception you would need to import and catch specifically. It doesn’t look like you get much info back (null) but at least catching this specifically you could start logging those instances and perhaps some sort of pattern that is causing it.
I’ve replaced mine with the java excepts now and we will see if I can capture it. Thank you for the help.
So far I’ve been unable to catch this error, I’ve tried putting the try/except in a few different places. It makes the most sense to me that it should be directly around the system.tag.writeBlocking call, such as this:
	try:
	except java.util.concurrent.TimeoutException, e:
		logger.warn("Java Timeout exception for plant %s %s %s" % (plant, deviceName, opName))
However this is not catching the error and it is still unhandled. I also tried putting it in the calling script that calls this function but that did not catch it either.
Are you calling writeBlocking from a Vision client? If so, the exception would be wrapped by a GatewayException. Consider catching java.lang.Throwable instead.
No, I’m using a tag event script to send a message to a project message handler which then calls a thread handler that dispatches the call to a thread pool.
Trivial but maybe important - you’re importing the java error? import java.util.concurrent.TimeoutException or import java.lang.Throwable. I don’t think you can reference them without importing them.
Correct, I am importing java.util.concurrent.TimeoutException
Another interesting note, is that these show up under the startup/shutdown gateway scripts logs, even though I do not have any gateway startup/shutdown scripts configured.
Click on the “+” sign to get the details to show us.
Hi Phil,
Hitting the plus just shows the error message that I pasted in the original post:
I’m going to guess you have more places to put try-except blocks. Please catch java.lang.Throwable instead of TimeoutException.
Ok, I just swapped them all over. I’ve wrapped every system.tag.writeBlocking I can find with it, but the exception actually references the next line after the system.tag.writeBlocking as the line that the error occurred on which is what is strange to me, and the next line is simply the beginning of my for loop.
Also, do you know if errors without a try/catch are raised to the calling functions try/catch clause? So for example if I have:
def callingFunction()
	try:
		someFunction(someArgs)
	except:
		print ("Failed")
def someFunction(someArgs)
	somethingThatCausesAnException()
If an error occurs in “someFunction”, will the error be caught by the try/catch of callingFunction or be reported in the gateway logs as an unhandled exception?
The error of someFunction will be caught by your except clause as long as it’s the right sort of except. For example
def callingFunction():
    try:
        someFunction()
    except TypeError,e :
         print "type error occured"
    except KeyError, e:
         print "key error occured"
def someFunction():
    d = {'someKey':'someValue'}
    return d['nonExistantKey']
someFunction will trigger a KeyError and you will see “key error occured”. You would also catch this with just a plain except or a except Exception, but if you don’t have except\except Exception\except KeyError, then the error will bubble up either to the GUI or to the gateway logs depending on where you are calling this function.
For the record this is how I do things. I created a custom error FormError that I raise inside functions when a user enters invalid input into forms, and on my GUI I try/except FormError when they are trying to create or update a record. Like
try:
    createForm(data)
except FormError, e:
    system.gui.messageBox(str(e))
Where createForm calls a list of functions some of which may raise a FormError.
So with knowing that, as long as I am excepting java.lang.Throwable and java.util.concurrent.TimeoutException in the calling script at the top of my hierarchy, I should be able to catch any unhandled errors of those two types from any call lower in the program stack, right?
If this is the case, that’s how I am doing it, I have one script, my thread handler, that dispatches all of the rest of the calls, so putting the try/except in my thread handler should catch everything, however I am still getting unhandled exceptions to the gateway via this method.
It’s pretty common practice to do try/except with multiple error clauses. That is correct though from your testing it seems like java.util.concurrent.TimeoutException is not working and it will come through as a java.lang.Throwable as @pturmel said.
You can make it separate if you want to see which one specifically is being triggered
try:
    system.tag.writeBlocking(...)
except java.lang.Throwable, e:
    # handle gracefully
    # also handle gracefully
In general though, as a little python 2 tidbit that you can use to help keep things more modular, you can catch and handle multiple errors in one except clause
try:
    # Do something
except (KeyError, TypeError), e:
    # Handle KeyError and TypeError the same way
This is helpful for when you want to handle multiple different error conditions the same way
So what I’ve done is removed all try/excepts from my writeBlocking calls and added a single try/except to the single call that handles all of the other calls in my project. I am excepting both errors listed above just like you have it:
    # handle gracefully
However, they are somehow STILL getting through to the gateway, not sure where to go from here.
writeBlockingImpl logs this exception and then returns error QualityCodes.
You guys are trying to catch something that is never thrown.
Thanks Kevin, do you have any suggestions on how I can diagnose this issue to find out exactly which tags are having write timeouts? It’s a parameterized UDT so it could be any PLC that I have that is causing this error.