COGNEX 9000 Series Camera / Sensor OPC Connection (9912)

Setting up Ignition OPC / Cognex OPC
IMPORTANT: Be sure Cognex camera firmware is updated to 5.07.03 (041) or later as the built in OPC server will not function in previous versions.

In-Sight Explorer application is needed to setup camera
Download here: Support - In-Sight Software & Firmware | Cognex
Activation Key will be needed after install
Found here: In-Sight Key Generator | Cognex

To edit network in Sensor dropdown, click on 'Get Connected'

Network Settings:

Select the OPC UA checkbox and copy the IP for Ignition in the network popup:
networkPopup

After creating tool sets for your critical data, click the Communications Button, select OPC and Add the Tags you want from the results

In the Ignition Gateway select OPC CLIENT / OPC Connections / OPC UA

Enter your IP address with port (Default:4840):

After setup complete browse devices from tag browser to pull in your new tags