Comm issues with ABB RMC-100 Flow computer

Ignition 8.1.47

I'm trying to connect our Ignition gateway to a ABB RMC-100 flow computer using the ABB TotalFlow driver from Cirrus-link. and have been having a number of difficulties I'm wondering how to troubleshoot.

The OPC UA connection is setup, connected, and has a status of polling yet in the Ignition logs I continually get errors related to DB2 registers. I've followed all the documentation for loading the provided files into the driver, all of the auto-discovery worked and pulled in the apps, and I'm able to read the array registers via OPC. This is for internal testing so they are located on the same network.

I do have the recommended MQTT modules installed however I temp disabled them for testing and it's still the same errors related to the DB2 registers with or without them. I also cut the logs off after a few cycles but it continues failing another ~30 times before stopping.

I'm unsure why I'm getting these errors or what they even mean? There isn't any configuration for Db2 registers that I can see aside from the station ID which is set to match the RTU. Figured I'd try the forums as well as contacting Cirrus for support incase anyone has run into this before.

Db2RegisterTransaction	15Apr2025 09:03:01	['test-rmc' 10.1.8.197:9999] Failed to receive DB2 Register reply Db2RegisterReply: [Status=TIMEOUT]. Retries left: 2
Db2RegisterTransaction	15Apr2025 09:03:01	['test-rmc' 10.1.8.197:9999] Timed out receiving DB2 Register reply
HistoryPoller	15Apr2025 09:02:58	['test-rmc' 10.1.8.197:9999] Failed to obtain Periodic history RecordSettings from Totalflow Device
RecordInfoPoller	15Apr2025 09:02:58	['test-rmc' 10.1.8.197:9999] Failed to obtain RecordInfo for AppSlotNum=146
Db2RegisterTransaction	15Apr2025 09:02:58	['test-rmc' 10.1.8.197:9999] Failed to receive DB2 Register reply Db2RegisterReply: [Status=TIMEOUT]. Retries left: 0
Db2RegisterTransaction	15Apr2025 09:02:58	['test-rmc' 10.1.8.197:9999] Timed out receiving DB2 Register reply
Db2RegisterTransaction	15Apr2025 09:02:55	['test-rmc' 10.1.8.197:9999] Failed to receive DB2 Register reply Db2RegisterReply: [Status=TIMEOUT]. Retries left: 1
Db2RegisterTransaction	15Apr2025 09:02:55	['test-rmc' 10.1.8.197:9999] Timed out receiving DB2 Register reply
Db2RegisterTransaction	15Apr2025 09:02:52	['test-rmc' 10.1.8.197:9999] Failed to receive DB2 Register reply Db2RegisterReply: [Status=TIMEOUT]. Retries left: 2
Db2RegisterTransaction	15Apr2025 09:02:52	['test-rmc' 10.1.8.197:9999] Timed out receiving DB2 Register reply
Db2RegisterTransaction	15Apr2025 09:02:46	['test-rmc' 10.1.8.197:9999] Failed to receive DB2 Register reply Db2RegisterReply: [Status=TIMEOUT]. Retries left: 2
Db2RegisterTransaction	15Apr2025 09:02:46	['test-rmc' 10.1.8.197:9999] Timed out receiving DB2 Register reply
HistoryPoller	15Apr2025 09:02:43	['test-rmc' 10.1.8.197:9999] Log Period 'Last Sequence Number Used' has changed for Application Slot Number 100 from 97 to 98. Scheduling one shot event for manual poll..
HistoryPoller	15Apr2025 09:02:43	['test-rmc' 10.1.8.197:9999] Log Period 'Last Sequence Number Used' has changed for Application Slot Number 145 from 23 to 24. Scheduling one shot event for manual poll..
HistoryPoller	15Apr2025 09:02:43	['test-rmc' 10.1.8.197:9999] Log Period 'Last Sequence Number Used' has changed for Application Slot Number 101 from 97 to 98. Scheduling one shot event for manual poll..
HistoryPoller	15Apr2025 09:02:43	['test-rmc' 10.1.8.197:9999] Log Period 'Last Sequence Number Used' has changed for Application Slot Number 147 from 22 to 23. Scheduling one shot event for manual poll..
HistoryPoller	15Apr2025 09:02:43	['test-rmc' 10.1.8.197:9999] Log Period 'Last Sequence Number Used' has changed for Application Slot Number 146 from 23 to 24. Scheduling one shot event for manual poll..
TransmissionRecordListener	15Apr2025 09:02:43	No TransmissionClient found for Group G1, Edge Node E1, Device RMC-01 - not publishing record
TransmissionRecordListener	15Apr2025 09:02:43	No TransmissionClient found for Group G1, Edge Node E1, Device RMC-01 - not publishing record
TransmissionRecordListener	15Apr2025 09:02:43	No TransmissionClient found for Group G1, Edge Node E1, Device RMC-01 - not publishing record
TransmissionRecordListener	15Apr2025 09:02:43	No TransmissionClient found for Group G1, Edge Node E1, Device RMC-01 - not publishing record
TransmissionRecordListener	15Apr2025 09:02:43	No TransmissionClient found for Group G1, Edge Node E1, Device RMC-01 - not publishing record
AbbTotalflowDriver	15Apr2025 09:02:43	['test-rmc' 10.1.8.197:9999] CFX File Transfer is not enabled. Make sure MQTT Transmission module is installed and Auto-FilePublish is configured.
AbbTotalflowDriver	15Apr2025 09:02:43	['test-rmc' 10.1.8.197:9999] Scheduling CFX File Transfer
TotalflowMeterConfig	15Apr2025 09:02:43	
AarPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] INI Parser Polls have been completed (status=SUCCESS) threadName=IniParserPoller-'test-rmc'-b1739c15-1, threadId=407361. Scheduling AAR polls ...
IniCondition	15Apr2025 09:02:42	Can't evaluate INI condition: opInd=0, ConditionalCode=null
IniCondition	15Apr2025 09:02:42	Can't evaluate INI condition: opInd=0, ConditionalCode=null
TotalflowSystem	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Totalflow Application auto-discovery thread stopped
TotalflowSystem	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Shutting down auto-discovery executor..
TotalflowSystem	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Cancelling the auto-discovery task..
AbstractRecordPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Scan Rate for the EventPoller is set to: 0. Not Scheduling polling
AbstractAbbPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Initializing EventPoller
AbstractRecordPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Scan Rate for the AlarmPoller is set to: -1. Not Scheduling polling
AbstractAbbPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Initializing AlarmPoller
AbstractAbbPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Initializing periodicHistoryPoller
AbstractAbbPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Initializing dailyHistoryPoller
AarPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] INI Parser Polls have been completed (status=TERMINATED) threadName=IniParserPoller-'test-rmc'-bf5f76d8-1, threadId=407356. Scheduling AAR polls ...
AarPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Servicing INI Variables poll groups..
AbstractAbbPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Initializing RecordInfo-Poller
AarPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Scheduling INI parser poll ...
AbstractAbbPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Initializing AarPoller
AarPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Initializing AarPoller
IniCondition	15Apr2025 09:02:42	Can't evaluate INI condition: opInd=0, ConditionalCode=null
IniCondition	15Apr2025 09:02:42	Can't evaluate INI condition: opInd=0, ConditionalCode=null
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Starting the ABB Totalflow polling
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] ABB Totalflow driver stopped
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Stopping Alarm Poller..
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Stopping Event Poller..
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Stopping History Poller..
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] 'Record Info' Poller stopped
AarPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Stopped servicing INI variables poll groups. The IniParserPoller-'test-rmc'-bf5f76d8-1 thread is being terminated
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Stopping 'Record Info' Poller..
AarPoller	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Servicing INI Variables poll groups..
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] AAR Poller stopped
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Stopping AAR Poller..
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Scheduler has been shuddown
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Shutting down scheduler..
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Stopping scheduled polls
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Stop Polling - REINITIALIZE
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Auto-discovery completed, restarting pollers..
TotalflowMeterConfig	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Starting MeterConfigPoller..
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Auto-discovery completed, starting MeterConfigPoller..
AbbTotalflowDriver	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Auto-discovery successfully completed, restarting polling
ArrayRegisterUtil	15Apr2025 09:02:42	['test-rmc' 10.1.8.197:9999] Can't find global definition for the TotalflowApplication: [Name=XIO Interface-80, SlotNumber=208, Enumeration=114, Revision=2106201-002, Parameter=Dir = \RXIO-1, PollingEnabled: false]
TotalflowSystem	15Apr2025 09:02:41	['test-rmc' 10.1.8.197:9999] Application auto-discovery completed successfully
AarPoller	15Apr2025 09:02:40	['test-rmc' 10.1.8.197:9999] Not executing INI parser poll - Totalflow Application auto-discovery is in progress
AbbTotalflowDriverType	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] The ABB Totalflow Driver has been started.
AbbTotalflowPeriodicMappingRecordListene	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] Adding the AbbTotalflowDriver as meter periodic mapping update listener
AbbTotalflowConfigMappingRecordListener	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] Adding the AbbTotalflowDriver as meter configuration mapping update listener
DeviceManager	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] ABB Totalflow Driver started
AbstractRecordPoller	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] Scan Rate for the EventPoller is set to: 0. Not Scheduling polling
AbstractAbbPoller	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] Initializing EventPoller
AbstractRecordPoller	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] Scan Rate for the AlarmPoller is set to: -1. Not Scheduling polling
AbstractAbbPoller	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] Initializing AlarmPoller
AbstractAbbPoller	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] Initializing periodicHistoryPoller
AbstractAbbPoller	15Apr2025 09:02:39	['test-rmc' 10.1.8.197:9999] Initializing dailyHistoryPoller
AarPoller	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Not executing INI parser poll - Totalflow Application auto-discovery is in progress
AbstractAbbPoller	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Initializing RecordInfo-Poller
AarPoller	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Scheduling INI parser poll ...
AbstractAbbPoller	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Initializing AarPoller
AarPoller	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Initializing AarPoller
TotalflowSystem	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Totalflow Application auto-discovery thread started
TotalflowSystem	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Starting Totalflow Application auto-discovery..
AbbTotalflowDriver	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] For ON_DEMAND connection, start auto-discovery before polling
AbbTotalflowDriver	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Starting the ABB Totalflow polling
AbbTotalflowDriver	15Apr2025 09:02:38	['test-rmc' 10.1.8.197:9999] Starting up AbbTotalflowDriver..
DeviceManager	15Apr2025 09:02:37	['test-rmc' 10.1.8.197:9999] The 'Configuration Mapping' ReferenceField is not set.
DeviceManager	15Apr2025 09:02:37	['test-rmc' 10.1.8.197:9999] Creating ABB Totalflow Driver.
ArrayRegisterUtil	15Apr2025 09:02:37	['test-rmc' 10.1.8.197:9999] Can't find global definition for the TotalflowApplication: [Name=XIO Interface-80, SlotNumber=208, Enumeration=114, Revision=2106201-002, Parameter=Dir = \RXIO-1, PollingEnabled: false]
AbbTotalflowDriverType	15Apr2025 09:02:36	Creating the ABB Totalflow Driver for test-rmc