Connect Modbus type floating point value is missing

Dear All
I have problem about connect tag from power meter
1.first step i use modscan for find value from power meter and i set display is(Floating Pt) value is OK
2.I Config addressing on gateway
3.But I read value from OPC Quick Client and value is missing

Help me please

I guess you should use "swap words" option for this device