We have our redundant connected to the master and it's synced and warm.
I can see it in the EAM but is showing disconnected. When I try to set up an outgoing connection in the redundant, I can't because it's set as a backup.
Does the master gateway push the EAM connection to the backup or do I need to setup the backup's outgoing connection to the EAM before connecting it to the master?
We've figured it out.
  1. Disconnect the Independent Gateway from the EAM
  2. Configure the Independent Gateway's redundancy settings to Master
  3. Configure the Backup Gateway's redundancy settings to Backup
  4. Pair the Master with the new Backup Gateway and approve the connection and certificate on the Master
  5. The Backup should synchronize with the Master and will likely restart the service.
  6. Connect the Master Gateway to the EAM and approved the connection and certificate on the EAM.
  7. After the Master Gateway is connected the EAM will receive an incoming connection request from the Backup.
  8. Approve the connection and certificate for the Backup Gateway on the EAM.
note: I could not find how to connect a redundant pair to the EAM in the documentation.
@hw79, I'm glad you got it sorted out. I was just compiling some information surrounding ticket IGN-7273 that we have in our system regarding transitioning an existing EAM Agent gateway to a redundant configuration. Currently, there are some manual steps required for this, namely removing the existing EAM Agent configuration from the controller and approving both the new -master and -backup suffixed agent entries you'll see appearing from the redundant gateway. Basically equivalent to the corrective actions you described. :+1: In the future, we're going to have that aspect of EAM Agent registration (upon transitioning to a redundant pair) happen more gracefully and automatically.
Just to clarify a couple other points for others visiting this thread in the future:
  • Transitioning the soon-to-be-backup gateway from Independent -> Backup redundancy role will initiate an outbound connection to the defined Master gateway.
  • Once that gateway network connection is approved on the Master gateway, redundancy will hook up and things will synchronize. Among those things are the EAM agent settings, pointing to the same controller.
  • The outgoing GAN connections will sync over to the Backup, and as such, you'll see a new incoming connection from the Backup gateway on your controller--this needs to be approved before the EAM Agent registration will appear.
  • This is where the workaround above might be required, you may need to first delete the existing Independent EAM Agent registration now that that gateway is configured as Master role in redundancy. Then re-approve the xxxx-Master EAM Agent registration.
  • Finally, approve the new xxxx-Backup EAM Agent registration once you're up and running.
Has there been any progress on this EAM issue?
The ticket IGN-7273 (titled "EAM: Changing an agent to use redundancy causes an orphaned non-redundancy agent") is still open in our system--at the moment, unless other efforts have improved this situation, you may still need to perform some additional steps (that I outlined above) to transition an agent to a redundant configuration.