I’m trying to connect to a MicroLogix 1400 v2.015 through the backplane of a CompactLogix 5069-L340ERMS2 v31.001(Dual IP Mode). The plant network is connected to port A1(172.20.0.x) and the IO network is on port A2(10.1.1.x). The MicroLogix is on the IO network.
I have tested the path(3, 172.20.0.10, 4, 10.1.1.2) and it works from another 5069-CompactLogix to the MicroLogix through the backplane.
The Ignition server(v8.0.11) is on the plant network and the device is it up like this:
Hostname: 10.1.1.2
Connection Path: 172.20.0.10,4
All I ever get is “Connecting: Determining Protocol” or “Disconnected: Determining Protocol”
I’m not sure what I’m missing here.
Thank you,
FYI I had to look this up as well.
When you configure a MSG instruction on a CompactLogix 5380 controller that operates in Dual-IP mode, use the following paths:
** Enterprise port (Port A1) - 3, IP address*
** Device-level port (Port A2) - 4, IP address*