Hello I have  a two PLC’s I will call them PLC1 and PLC2.  PLC 1 is on our Plantwide network but PLC2 is not.
PLC2 is hooked up to a separate card that is in Slot 15 off of PLC1. I need to come up with a  path for the UPC-UA Device.
PLC1 Address is 192.168.0.1 ENBT Allen Bradly card
PLC2 address is 192.168.75.14 ENBT Allen Bradley card
The Hostname path I am trying to write is
192.168.0.1,1,15,2,192.168.75.14,2,1,0
192.168.0.1- first Ethernet address to browse
1=backplane
15=Ethernet card slot number on plc1
2=port#
192.168.75.14=address of PLC2 Ethernet card
2= Port#
1 =backplane
0=cpu slot #
I have tried different port #s as well. but have not found much info on this.