Is there a way to assign a tag an Alarm template?
Or a way to copy and paste the configured alarms from a tag to another?
I have several tags with the same logical alarm abd i would not set them one by one…
Thnk you
I have a similar tag structure, alarm1, alarm1, etc… I used scripting to loop through the tags and set everything i needed, with the exception of alarms as they are very dynamic based on what each alarm needs.
To add alarms, I built one the normal way, exported it in xml to get the structure and then used a script to make as many as i needed and then imported the new tags in.
I hope one of these ways works for you
Thank you for the response.
It’s a bit tricky… i have several alarm classes, and it would be not so time-saving.
the best way to configure them would be having a bindable template (as for the UDT).
another solution would be copying and pasting the conf from a tag to another, even if it’s one way…
drewdin’s suggestion is a great way to do this. I think an XML export of your SQLTags, then adding the alarms to the export, would be an efficient way.
You can just copy and paste the alarm itself. Even though you cannot display the right click menu on the alarm, you can actually copy it with ctrl-c when you select it. Then go to the tag where you want the alarm you just copied, click on the new alarm to select it, and then do ctrl-v and it will copy the alarm. Hope this helps. I'm using 8.1.41, not sure if it works the same for older versions.
Fantastic! Saved me a lot of time!
Alarm configuration on a UDT member would work here as well.