Could someone help integrate energy meter ION 7400 to Ignition using Modbus TCP

Hi everyone..!
We have energy meter ION 7400.
We have a mapping adreses, e.g. the frecuency is 3110 and use 2 register.
I see on modbus pool on 2 register 43110 and 43111
I dont know how to integrate. Could help us? about it.

The Modbus register map Schneider has doesn't show frequency on those addresses, they have those as belonging to a data recorder module. I've got some ION 6200 meters connected to ignition, maybe if you tell us more about what you are trying to do we can take a closer look.

Maybe this helps, this is an example for an ion9000