First step is to connect to the device from Ignition’s OPC-UA server with a device driver. The driver/protocol will depend on the PLC type and model. What device are you using?
modbus opc tags
bmxp34 2020
Have you looked over the user manual for modbus device setup?
Do your counters have modbus addresses assigned in Control Expert? Ignition cannot reach memory that doesn't.
yes i have discreer inputs already connected just having trouble pulling or addressing timer correctly i am using a hr_ adresss modbus adress is a %mw adress
Show the Control Expert settings where you assign a word memory address to your counters. It isn't visible in your first screenshot.
here is a adress from a analog imput we have adressed that works properly
OK. Try manually creating Ignition OPC tags with one of these OPC Item Paths:
[ProcessingMainChain]HR334.0
[ProcessingMainChain]HR335.0
[ProcessingMainChain]HR336
or possibly:
[ProcessingMainChain]HR333.0
[ProcessingMainChain]HR334.0
[ProcessingMainChain]HR335