I have an issue regarding data from a named query that appears to be caching, even though caching is not set.

I have an SFC that runs a loop, the loop has a 2-second delay, then if it’s “ok to do data verification” it calls a script which does the data verification. Once that is done, it returns to the delay and loops again

The data verification script does a named query and compares the result to the data in PLC tags.

This all works fine, But if we pause the loop while we update the data in the database and the PLC and then start the loop again, the data that the script is bringing back from the database is the old value. I have tried lengthening the timer, and I can see through SSMS that the data in the database has changed but the named query appears to have the old data.

The ‘Cache Query Results’ in the named query is not enabled

Script (data verification)

sourceFunction= usrFunc.functionName()
strBatch = str(system.tag.readBlocking(['Batch/Data/selectedBatchID'])[0].value)
intRecipe = system.tag.readBlocking(['Batch/Data/Recipe/RecipeID'])[0].value
currStep = system.tag.readBlocking(['Batch/Sequence/Main/iState'])[0].value
skipValidation = system.tag.readBlocking(['Batch/Sequence/Main/skipParamValid'])[0].value
lineName = system.tag.readBlocking(['Batch/Sequence/lineName'])[0].value
#Query active parameters listed on DB
namedQuery = "SFC/get_ActiveParams"
dsActiveParams=system.dataset.toPyDataSet(system.db.runNamedQuery(namedQuery,{'line':lineName}))

*#Iterate DS to get mismatch between DB and OPC*
result = \[\]
**for** index, row **in** enumerate(dsActiveParams):
    *#Read OPC path and get formatted data*
    tries = 0
    tagRead = \[None\]
    **while** (tries <=3) **and** (tagRead\[0\] == None):
        tagRead = utils.opcReadValue(row\['TagUrlRead'\],0,opcServerName)
        tries += 1
    *#Compare erading against SP*
    matchEval = (str((row\['SetPoint'\])) == str(tagRead\[0\])) & ('Good' == str(tagRead\[1\].quality))
    **if** matchEval != True:
        evaluation = \['Tag: '+str(row\['Tag'\]),'DBValue: '+str(row\['SetPoint'\]),'FromPLC: '+str(tagRead\[0\]),'OPCQuality: '+str(tagRead\[1\].quality)\]
        result += \[evaluation\]

*#Function will return False or empty List if No Difference found*
**if** (len(result) != 0) **and** (skipValidation == 0):
    **if**  listMismatch == False:
        **return** True
    **else**:
        **return** result
**else**:
    **if**  listMismatch == False:
        **return** False
    **else**:
        **return** \[\]

Named Query (SFC/get_ActiveParams)

SELECT
[Tag],
IIF([DataType] LIKE 'String%', [StringSetPoint], CAST([NumericSetPoint] AS NVARCHAR(30))) AS [SetPoint],
IIF([DataType] LIKE 'String%', '', CAST([NumericLowLimit] AS NVARCHAR(30))) AS [LowLimit],
IIF([DataType] LIKE 'String%', '', CAST([NumericHighLimit] AS NVARCHAR(30))) AS [HighLimit],
[TagUrlWrite],
[TagUrlRead],
[DataType]
FROM
[BatchData].[dbo].[Tag_Parameter_Active_Data]
WHERE
LineName LIKE :line;

Please edit your post and fix the formatting using the </> button. You've lost indentation and syntax highlighting on both your Python code and SQL query. See Wiki - how to post code on this forum.

1 Like

Formatted script and Named Query as requested

 	sourceFunction= usrFunc.functionName()
	strBatch = str(system.tag.readBlocking(['Batch/Data/selectedBatchID'])[0].value)
	intRecipe = system.tag.readBlocking(['Batch/Data/Recipe/RecipeID'])[0].value
	currStep = system.tag.readBlocking(['Batch/Sequence/Main/iState'])[0].value
	skipValidation = system.tag.readBlocking(['Batch/Sequence/Main/skipParamValid'])[0].value
	lineName = system.tag.readBlocking(['Batch/Sequence/lineName'])[0].value
	#Query active parameters listed on DB
	namedQuery = "SFC/get_ActiveParams"
	dsActiveParams=system.dataset.toPyDataSet(system.db.runNamedQuery(namedQuery,{'line':lineName}))
	
	#Iterate DS to get mismatch between DB and OPC
	result = []
	for index, row in enumerate(dsActiveParams):
		#Read OPC path and get formatted data
		tries = 0
		tagRead = [None]
		while (tries <=3) and (tagRead[0] == None):
			tagRead = utils.opcReadValue(row['TagUrlRead'],0,opcServerName)
			tries += 1
		#Compare erading against SP
		matchEval = (str((row['SetPoint'])) == str(tagRead[0])) & ('Good' == str(tagRead[1].quality))

		if matchEval != True:
			evaluation = ['Tag: '+str(row['Tag']),'DBValue: '+str(row['SetPoint']),'FromPLC: '+str(tagRead[0]),'OPCQuality: '+str(tagRead[1].quality)]
			result += [evaluation]
	#Testing system.util.getLogger('PLC Validation').info('Validation End ' + str(system.date.getMillis(system.date.now())))#Testing
	#Function will return False or empty List if No Difference found
	if (len(result) != 0) and (skipValidation == 0):
		if  listMismatch == False:
			return True
		else:
			return result
	else:
		if  listMismatch == False:
			return False
		else:
			return []


Named Query

SELECT 
    [Tag],
    IIF([DataType] LIKE 'String%', [StringSetPoint], CAST([NumericSetPoint] AS NVARCHAR(30))) AS [SetPoint],
    IIF([DataType] LIKE 'String%', '', CAST([NumericLowLimit] AS NVARCHAR(30))) AS [LowLimit],
    IIF([DataType] LIKE 'String%', '', CAST([NumericHighLimit] AS NVARCHAR(30))) AS [HighLimit],
    [TagUrlWrite],
    [TagUrlRead],
    [DataType]
FROM 
    [BatchData].[dbo].[Tag_Parameter_Active_Data]
WHERE 
    LineName LIKE :line;

You posted it twice. The original mess is still there!
I suggest you remove the code blocks from the original post to keep the thread tidy.

It will not let me edit the original post - I can edit my replies but not the original post

Ah! OK. It may be something to do with your number of posts on the site determined by the forum.
Don't worry about it.

Can you answer to those question:

  • Did you validate the query output with a log?
  • When updating the database, do you add lines, or you update the existing one?
  • Did you restart the SFC after your last code change?

Recommendation: individual readBlocking and individual OPC read are expensive, combine them to have a single tag read and a single opc read

  • not sure what you mean by -
  • When updating the database we update an existing row with an update query
  • yes the SFC was restarted since the last code update. In fact the gateway has been restarted even.

Get a logger using system.util.getLogger, then do a logger.debugf(“some value I change in the database: %s”, str(dsActiveParams[0][5]))