DNP3 comms only giving 3 Analog input tags

I have just started to set up an alarm system Micro 870 DNP3 to Igntion. but I can only get data on the first 3 analog input tags. I have looked for some logic in the setups but nothing seems to tie to this. The same happened on a kingfisher test rig

If you post the setup you have tried, and the tag config, it might help, also any error messages?

Any particular reason you don't just use the Micro800 driver?

Yes sorry I didn’t really layout any of the architecture. We are gathering data from a range of Rockwell PLCs in the field, using either a siemens or Micro870 as an RTU to pass data via IP radios to the Ignition system . DNP3 also has the data storing capability we like in water waste systems

Make sure you're using the new DNP3 driver and not the legacy one.

Any points you see in the OPC Browse are going to be determined by what the outstation returns during the initial integrity poll, so check the configuration of the outstation and maybe get a Wireshark capture if it doesn't match your expectations.

Sorry if I have them out of order but thta is the setups of both the 870 and ignition

Thank you ,

Yes I have it set for the latest DNP not legacy