I’m sure this an easy one for the right person! I’m integrating SEL protection relays via DNP3 into ignition and then passing to another SCADA system via OPC.
The accumulative energy value has stalled at 32767, even though in the originating device it has continued to increase.
Its currently reading as a Datatype: Double and OPC Item Path is ns=1;s=[{Device}]AnalogInput16
Thanks gents, I’ve experienced this with Modbus, but I’m new to DNP3. I don’t think I have a lot of configuration options in the originating device as its not mine unfortunately!
If you have access to the relay, I’d suggest downloading SEL AcSELerator QuickSet (free with a selinc.com account) and see if you can read the settings file from the meter, and look at the configuration for your DNP3 connection(s).