Hello everyone, I am new to Ignition Scada. I do not have PLC physically. I have connected simulator of Delta PLC ISPsoft with ignition scada. I have connected via MODBUS TCP. I also got all tags in designer. But these tags are not showing values of 1 or 0 even after connecting with path....


[Delta]Y0 isn't a valid Modbus address.
Try something like:
[Delta]HR1[Delta]1.HR
See Modbus Addressing - Ignition User Manual 8.1 - Ignition Documentation
Do you have any other Modbus client that can connect and read?
No, I am trying to connect simulator with Ignition scada. And i think both will have same local ip address but different port?
Try addressing unit/slave id 1 instead of 0.
Try with another software like Modscan or Modpoll.
Hello.
What is the ID for DVP Simulator?
Thank you.
Best regards.