Error Writing to PLC Tags : Bad_Failure
Hello,
Recently facing an issue while writing to PLC.
Gateway Logs - INFO | jvm 1 | 2019/10/10 10:03:07 | W [d.L.L.LogixBrowse ] [14:03:07]: Error browsing template instanceId=1369 device-name=Line 5
INFO | jvm 1 | 2019/10/10 10:03:07 | java.lang.Exception: senderContext=56122 timed out waiting 2000ms for response
INFO | jvm 1 | 2019/10/10 10:03:07 | at com.digitalpetri.enip.EtherNetIpClient.lambda$writeCommand$5(EtherNetIpClient.java:168)
INFO | jvm 1 | 2019/10/10 10:03:07 | at io.netty.util.HashedWheelTimer$HashedWheelTimeout.expire(HashedWheelTimer.java:682)
INFO | jvm 1 | 2019/10/10 10:03:07 | at io.netty.util.HashedWheelTimer$HashedWheelBucket.expireTimeouts(HashedWheelTimer.java:757)
INFO | jvm 1 | 2019/10/10 10:03:07 | at io.netty.util.HashedWheelTimer$Worker.run(HashedWheelTimer.java:485)
INFO | jvm 1 | 2019/10/10 10:03:07 | at java.base/java.lang.Thread.run(Unknown Source)
INFO | jvm 1 | 2019/10/10 10:07:11 | E [LegacyScripting[system_util_tag]] [14:07:11]: Error writing tags
INFO | jvm 1 | 2019/10/10 10:07:11 | Error writing to tag ‘[default]EF7842_Line5/Test/Pass’: Bad_Failure
INFO | jvm 1 | 2019/10/10 10:07:42 | I [g.LicenseManager ] [14:07:42]: Trial time reset. Time remaining = 7200. route-group=status, route-path=/trial
INFO | jvm 1 | 2019/10/10 10:21:46 | W [P.WebSocketChannel ] [14:21:46]: Websocket connection closed unexpectedly. code=1006, reason=WebSocket Read EOF
INFO | jvm 1 | 2019/10/10 10:21:46 | I [p.DesignSession ] [14:21:46]: WebSocket disconnected from session. session-project=Line5_Test
INFO | jvm 1 | 2019/10/10 10:24:52 | W [s.ProjectRunner ] [14:24:52]: Tried to perform RPC operation on an unrecognized session. May indicate that the previous session was lost. Creating RPC listener for new session id. project-name=Line5, request-origin=xx.xx.xx.xxx, session-user=, session-project=Line5, session-id=
INFO | jvm 1 | 2019/10/10 10:25:03 | E [LegacyScripting[system_util_tag]] [14:25:03]: Error writing tags
INFO | jvm 1 | 2019/10/10 10:25:03 | Error writing to tag ‘[default]EF7842_Line5/Test/Pass’: Bad_Failure
INFO | jvm 1 | 2019/10/10 10:26:23 | E [LegacyScripting[system_util_tag]] [14:26:23]: Error writing tags
INFO | jvm 1 | 2019/10/10 10:26:23 | Error writing to tag ‘[default]EF7842_Line5/Test/Pass’: Bad_Failure
Restarting the VM fixed the issue. Any suggestions on how to fix this?
Any feedback would be greatly appreciated.
Thanks,
Hello,
I have same issue .
When I’m writing value by script to opc tag it shows error “LegacyScripting[system_util_tag]] [14:26:23]: Error writing tags:bad_unsupported.”
But it write value correct value to opc tag
Is it affect to system?
When I’m using internal memory tag instead of opc tag it’s don’t show error.
@dhirajpawar371 - There are many changes we implemented to get rid of such error.
  • Increase the number of Max Concurrent requests to 16 under Config-> OPC UA-> Device Connection -> your PLC.
  • Avoid changing PLC logic when Ignition script is trying to the same tags
  • Also, make sure not to overload PLC, Check Load Factor under Status -> Devices -> Your PLC. Make sure its less than 10-15%. If it’s more try reducing the number of OPC servers connected to this PLC