Hi All,
I’m trying to setup an easy chart to only display pen data when a particular event has occurred. My pens are
Pens:
-pH
-Temperature
Event (only display data when this event is true):
-Valve Open
There must be basic way to do this ?
Hi All,
Pens:
-pH
-Temperature
-Valve Open
The Tag History system stores samples individually, and without any reference to the conditions of other tags. The SQL Bridge’s transaction groups do, as it stores multiple values per row. With transaction groups, two simple solutions are possible:
Thanks Pturmel,
I thought where clause might have been the answer but it did not seem to work for me earlier today. I’ll check over things again in the morning. I used an expression binding for the where clause {valve open tag}=1, I assume that is ok?
No. A pen's where clause must be in SQL format, as the database actually executes it when the EasyChart retrieves the data. If you mean as a transaction group trigger condition, no, you must set up an execute-always item in the transaction group, and use it in the trigger settings for the group.