Execute Transaction Group from Script
Is there a way to execute a transaction group from a script?
Have a look in the manual.
https://docs.inductiveautomation.com/display/DOC80/Understanding+Transaction+Groups#UnderstandingTransactionGroups-TriggerandHandshakeSettings
Look at the trigger option and see if you can create a binding on the trigger condition to use the same thing that's triggering your script.
Otherwise give us more details on your setup.
Actually I have a memory tag connected to a Gateway Scheduled Script that runs Monday to Friday at 3:58 pm, this scripts activates the tag and there for activates the transaction group, I was just asking if there’s a way to directly execute the transaction group from the script.
Without the need of the trigger.
There is no way to directly trigger a transaction group from a script.
However, you could just use a scheduled trigger and have the transaction group configured to execute on the needed schedule.
Understanding Transaction Groups - Schedule
Create boolean variable.
Create transaction group with a trigger linked to this variable.
When script is executed, use system.tag.write to modify value of this boolean.
If you are going to write a script, have it do the entire operation. Skip having the transaction group entirely. Don't screw around with trigger tags--resetting afterwards reliably, without double executions or missed executions, is difficult to get right.