Expression Tag - Error_ExpressionEval
I have the script with throw a error_expressioneval. Runs fine in the script console.
Not sure where is the script error. Attached screenshot of expression tag.
def GenPE():
# Define variables
path1 = 'xx/ATS-01-PR-A/POS'
path2 = 'xx/MPE'
path3 = 'xx/MPE_Previous'
path4 = 'xx/PE'
path5 = 'xx/RUN'
tag1 = system.tag.readBlocking(path1)
tag2 = system.tag.readBlocking(path2)
tag3 = system.tag.readBlocking(path3)
tag4 = system.tag.readBlocking(path4)
tag5 = system.tag.readBlocking(path5)
atspos=tag1[0]
mpe=tag2[0]
mpe_prev=tag3[0]
gpe=tag4[0]
run=tag5[0]
pediff=0
if atspos.value==2 and run.value==0:
	pediff = mpe.value - mpe_prev.value
	gpe.value = pediff + gpe.value
	system.tag.writeBlocking(path4, gpe)
system.tag.writeBlocking(path3, mpe)
return gpe.value
energy
energy1
I can't see the problem (yet) but here are a few tips:
  1. See Wiki - how to post code on this forum. Yours is almost OK except for the first line.
  2. system.tag.readBlocking() expects a list of tag paths so even when there is only one it should be in [ ] brackets.
  3. Since system.tag.readBlocking can handle a list you do them all at once.
    tagPaths = ['xx/ATS-01-PR-A/POS',
                'xx/MPE',
                'xx/MPE_Previous',
                'xx/PE'.
                'xx/RUN'
    tagValues = system.tag.readBlocking(tagPaths)
Your code would then need to reference tagValues[0], etc.
  1. You also need [ ] lists on the writeBlocking line.
    system.tag.writeBlocking([tagPaths[2]], [mpe])
In current Ignition version the functions work when only one parameter is supplied (not in a list) but it's undocumented and could be "fixed" in the future.
A further thought - and this might be the problem: The script needs to be on the gateway, not in your project, otherwise the tag event can't find it. Where have you stored the script?
I also don't see why this calculation needs to be in a script. Why not perform the calculation directly in the expression on the expression tag? Seems that all the input tags have the same base path which could be parameterised.
It will accept a single string as well. It still returns a list though.
Your point #3 is valid however and is definitely the way the script should be written.
Thanks for the reply. Implemented with script configured as a scheduled gateway event.