I can't see the problem (yet) but here are a few tips:
- See Wiki - how to post code on this forum. Yours is almost OK except for the first line.
system.tag.readBlocking()expects a list of tag paths so even when there is only one it should be in[ ]brackets.- Since
system.tag.readBlockingcan handle a list you do them all at once.
tagPaths = ['xx/ATS-01-PR-A/POS',
'xx/MPE',
'xx/MPE_Previous',
'xx/PE'.
'xx/RUN'
tagValues = system.tag.readBlocking(tagPaths)
Your code would then need to reference tagValues[0], etc.
- You also need
[ ]lists on the writeBlocking line.
system.tag.writeBlocking([tagPaths[2]], [mpe])
In current Ignition version the functions work when only one parameter is supplied (not in a list) but it's undocumented and could be "fixed" in the future.
A further thought - and this might be the problem: The script needs to be on the gateway, not in your project, otherwise the tag event can't find it. Where have you stored the script?