I’m trying to access a dynamic address from a 1500 Siemens PLC. It should be something like
[PLCName]DB50,Real300*(2+n). Where n is a variable that actually comes from another tag. So:
[PLCName]DB50,Real(300*(2+{Tagxx})).
But I can’t get it working. Which type of tag should it be? An OPC Tag or an Expression tag? Can I access an address this way?
I’ve seen the Indirect Tag binding, but I’m not sure if this fits for that case.
PD: the type of data located in this address is a real. Which Data Type for the Tag should I select? A float or a Double?
No, you cannot make an OPC Item Path depend on another tag like this. If it doesn’t change often, you can use a change script on the other tag to rewrite the OPC Item Path on the desired tag, but note that the tag restarts, with a noticeable delay.
Typically, users would create tags for all of the values and just pick the tag dynamically.
Thanks Pturmel!
Creating a tag for all the values it’s not the best approach, I think, because the auxiliary value can take up to 50 different values.
I’m trying to make a script to rewrite the OPC Item Path. I believe I can handle the delay.
But I’m not sure about how to do it, I haven’t used any Tag script yet. On value change event, I’ve tried:
[.]Tag_Name.tagPath = tag(‘ns=1;s=[PLC_Name]DB50,D’,currentValue)
where currentValue=300*(2+{Tagxx})
or it works just doing: [.]Tag_Name.tagPath = concat(‘ns=1;s=[PLC_Name]DB50,D’,currentValue) ?