"Gateway Comm Mode is not Read/Write" error in clients?

I have been noticing this problem on a big project of ours. Occasionally users of our client are reporting that sometimes when they click a button/field that executes a write to the PLC, they get an error that says “Gateway Comm Mode is not Read/Write”. Typically this is fixed by them just relaunching their client. Any idea what might cause this? I don’t really like telling the users to simply just “reboot the client”.

Thanks!

1 Like

This is the same thing that happens in the Designer when you use the button up top to toggle between read-only and read-write, except in the client there’s no button, so you might have a script somewhere that is setting the mode (system.util.setConnectionMode).

1 Like

Kevin,

Wow. Thanks for the heads up. I searched through our project and found at least one instance of that command in a random popup. I got it fixed now! Thanks again.