I want to run a script on gateway for the following time - (0,1,2,3,4,5,6,7,8,9,10,11,12,13:30,22:30,23) what inputs should I enter in Gateway Schedule Scripts console ?
I think you have two options:
- Create two schedules:
0 0-12,23 * * *for the on-the-hour events.
30 13,22 * * *for the 30 minutes past the hour events.
Both would call the same script. This has the disadvantage that you have to maintain two copies of the script. - Run the script every 30 minutes and exit out if it's not one of the required times.
0,30 * * * *
The script could be something like this (but the Python guys should be able to improve it):
hh = system.date.getHour24(system.date.now())
mm = system.date.getMinute(system.date.now())
# 13:30 and 22:30
if mm == 30:
if not hh in [13, 22]:
exit()
else:
if not hh in [0, 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 23]:
exit()
# Add your script here.
Didn't get the Second approach. Request to explain a bit more
Do you understand how to run the script every 30 minutes useing Project Browser | Scripting | Gateway Events | Scheduled?
The script is added on the Scheduled Script | Script tab.
Do you understand the script itself? If not where are you stuck?
Got it everything now.
Good. Try it out. If it works then mark post #2 as "Solution". Thanks.
Sure