Gateway Slow Startup
I've been having an issue with our dev gateway startup time, currently sitting at 22 mins..
Please see wrapper log below during startup. Seems like it's related to the OPC client, maybe something to do with the networking on the sever - we have a few NICs, and are multihoming IPs for Echo emulators.
Thanks,
Shea
STATUS | wrapper  | 2026/08/26 09:56:35 | --> Wrapper Started as Service
STATUS | wrapper  | 2026/08/26 09:56:36 | Java Service Wrapper Standard Edition 64-bit 3.5.60
STATUS | wrapper  | 2026/08/26 09:56:36 |   Copyright (C) 1999-2024 Tanuki Software, Ltd. All Rights Reserved.
STATUS | wrapper  | 2026/08/26 09:56:36 |     https://wrapper.tanukisoftware.com
STATUS | wrapper  | 2026/08/26 09:56:36 |   Licensed to Inductive Automation for Inductive Automation
STATUS | wrapper  | 2026/08/26 09:56:38 | Launching a JVM...
INFO   | jvm 1    | 2026/08/26 09:56:38 | WARNING: Unknown module: ALL-UNNAMED+ specified to --add-opens
INFO   | jvm 1    | 2026/08/26 09:56:39 | WrapperManager: Initializing...
INFO   | jvm 1    | 2026/08/26 09:56:42 | Scheduling logfile maintenance. Last maintenance: Wed Dec 31 19:00:00 EST 1969, events since then: 0
INFO   | jvm 1    | 2026/08/26 09:56:42 | Starting logfile maintenance. Max entries: 50000, Max filesize: 104857600
INFO   | jvm 1    | 2026/08/26 09:56:42 | Cleaned up 1374 rows in 27 ms. Vacuum performed: false
INFO   | jvm 1    | 2026/08/26 09:56:42 | I [g.CompositeClassRejectListFilter] [09:56:42.346]: Initialization performed successfully
INFO   | jvm 1    | 2026/08/26 09:56:42 | I [g.CompositeClassRejectListFilter] [09:56:42.355]: JVM-wide ObjectInputFilter set up successfully
INFO   | jvm 1    | 2026/08/26 09:56:42 | I [g.CompositeClassRejectListFilter] [09:56:42.356]: Platform serialFilter has 88 pattern(s)
INFO   | jvm 1    | 2026/08/26 09:56:42 | I [IgnitionGateway               ] [09:56:42.434]: Created DefaultSystemEncryptionService
INFO   | jvm 1    | 2026/08/26 09:56:42 | W [WebResourceManagerImpl        ] [09:56:42.898]: Unable to read "gateway.metroKeystoreAlias" gateway.xml property. Assuming metro keystore alias is: metro-key
INFO   | jvm 1    | 2026/08/26 09:56:43 | I [g.WebServerManager            ] [09:56:43.211]: Starting setup
INFO   | jvm 1    | 2026/08/26 09:56:43 | I [g.WebServerManager            ] [09:56:43.214]: Setup complete
INFO   | jvm 1    | 2026/08/26 09:56:43 | I [g.WebServerManager            ] [09:56:43.847]: Starting up
INFO   | jvm 1    | 2026/08/26 09:56:44 | I [C.SecureRandomProvider        ] [09:56:44.046]: Secure random seed generated in 0ms
INFO   | jvm 1    | 2026/08/26 09:56:44 | I [o.e.j.s.Server                ] [09:56:44.048]: jetty-12.0.34; built: 2026-04-01T05:45:03.823Z; git: 57e7adb250592bd15f573e7820be9b64632c6637; jvm 17.0.19+10-LTS
INFO   | jvm 1    | 2026/08/26 09:56:44 | I [o.e.j.s.DefaultSessionIdManager] [09:56:44.491]: Session workerName=node0
INFO   | jvm 1    | 2026/08/26 09:56:44 | I [o.e.j.s.h.ContextHandler      ] [09:56:44.500]: Started cic.IgnitionServer$IgnitionWebAppContext@4c35adfb{Ignition,/,b=file:///C:/Program%20Files/Inductive%20Automation/Ignition/webserver/webapps/main/,a=AVAILABLE,h=oeje10s.SessionHandler@36296bc8{STARTED}}
INFO   | jvm 1    | 2026/08/26 09:56:44 | I [IgnitionGateway               ] [09:56:44.503]: Ignition[state=STOPPED] ContextState = STARTING
INFO   | jvm 1    | 2026/08/26 09:56:44 | I [IgnitionGateway               ] [09:56:44.505]: Starting Ignition 8.3.8 (b2026071409)
INFO   | jvm 1    | 2026/08/26 09:56:44 | I [R.StateMonitoring             ] [09:56:44.645]: Redundancy state changed: Role=Independent, Activity level=Active, Project state=Good, History level=Full redundant-provider=system
INFO   | jvm 1    | 2026/08/26 09:56:45 | I [o.e.j.e.s.ServletContextHandler] [09:56:45.341]: Started cic.IgnitionServer$IgnitionWebAppContext@4c35adfb{Ignition,/,b=file:///C:/Program%20Files/Inductive%20Automation/Ignition/webserver/webapps/main/,a=AVAILABLE,h=oeje10s.SessionHandler@36296bc8{STARTED}}
INFO   | jvm 1    | 2026/08/26 09:56:45 | I [g.InternalDatabaseManager     ] [09:56:45.390]: Starting up...
INFO   | jvm 1    | 2026/08/26 09:56:45 | I [o.e.j.s.AbstractConnector     ] [09:56:45.415]: Started ServerConnector@6732093f{HTTP/1.1, (http/1.1)}{0.0.0.0:8088}
INFO   | jvm 1    | 2026/08/26 09:56:45 | I [P.InternalDatabase            ] [09:56:45.421]: internal database "config.idb" started up successfully.
INFO   | jvm 1    | 2026/08/26 09:56:45 | I [P.InternalDatabase            ] [09:56:45.421]: Registering autobackup task [owner=Internal DB Autobackup, name=internal database "config.idb"]
INFO   | jvm 1    | 2026/08/26 09:56:45 | I [o.e.j.s.AbstractConnector     ] [09:56:45.753]: Started ServerConnector@2f768113{SSL, (ssl, http/1.1)}{0.0.0.0:8060}
INFO   | jvm 1    | 2026/08/26 09:56:45 | I [o.e.j.s.Server                ] [09:56:45.755]: Started oejs.Server@5039849b{STARTING}[12.0.34,sto=10000] @7009ms
INFO   | jvm 1    | 2026/08/26 09:56:46 | I [SystemInfo                    ] [09:56:46.084]: os.name="windows server 2016", os.arch="amd64".
INFO   | jvm 1    | 2026/08/26 09:56:46 | I [SystemInfo                    ] [09:56:46.084]: Validating native library "ignition64"...
INFO   | jvm 1    | 2026/08/26 09:56:46 | I [SystemInfo                    ] [09:56:46.092]: Validated ignition64 (ignition64.dll)
INFO   | jvm 1    | 2026/08/26 09:56:46 | I [SystemInfo                    ] [09:56:46.092]: Loading native library "ignition64"...
INFO   | jvm 1    | 2026/08/26 09:56:46 | I [SystemInfo                    ] [09:56:46.095]: Native library load complete
INFO   | jvm 1    | 2026/08/26 09:56:46 | I [g.ModuleManager               ] [09:56:46.109]: Loading modules....
INFO   | jvm 1    | 2026/08/26 09:56:50 | I [g.SecretProviderManager       ] [09:56:50.143]: Setup complete in 0 ms
INFO   | jvm 1    | 2026/08/26 09:56:51 | I [g.ConfigurationManager        ] [09:56:51.532]: Config mode not set, loading 'core'
INFO   | jvm 1    | 2026/08/26 09:56:52 | I [c.i.i.g.c.m.MigrationLog      ] [09:56:52.261]: No migration strategies were executed, no migration log will be written.
INFO   | jvm 1    | 2026/08/26 09:56:52 | I [g.SecurityLevelManager        ] [09:56:52.319]: Setup completed in 0 ms
INFO   | jvm 1    | 2026/08/26 09:56:52 | I [g.OAuth2ClientManager         ] [09:56:52.319]: Setup complete in 0 ms
INFO   | jvm 1    | 2026/08/26 09:56:52 | I [g.IdentityProviderManager     ] [09:56:52.320]: Setup complete in 0 ms
INFO   | jvm 1    | 2026/08/26 09:56:52 | I [P.InternalDatabase            ] [09:56:52.469]: internal database "valueStore.idb" started up successfully.
INFO   | jvm 1    | 2026/08/26 09:56:52 | I [t.m.provider                  ] [09:56:52.590]: Setup managed tag provider 'System'. Settings=ManagedTagProviderConfiguration{name='System', allowTagCustomization=true, allowTagDeletion=false, persistTags=false, allowDefaultWriteHandling=false, synchronizeMemoryValues=false, enableTagReferenceStore=true, staleTimeout=0, attributes=Flags[260], mountPath='Gateway', valuePersistence=None, preserveDbTimestamp=false, initialDbQuality=null}
INFO   | jvm 1    | 2026/08/26 09:56:52 | I [c.i.i.g.t.r.StatefulTagReferenceStore] [09:56:52.668]: Creating and enabling new tag reference store for provider: System
INFO   | jvm 1    | 2026/08/26 09:56:52 | I [g.EmailProfileManager         ] [09:56:52.738]: Setup complete in 0 ms
INFO   | jvm 1    | 2026/08/26 09:56:53 | I [G.Manager                     ] [09:56:53.469]: Setting up trust list managers...
INFO   | jvm 1    | 2026/08/26 09:56:53 | I [G.Manager                     ] [09:56:53.483]: Trust list managers setup completed in 13 ms
INFO   | jvm 1    | 2026/08/26 09:56:57 | I [g.ModuleManager               ] [09:56:57.254]: Setting up modules
INFO   | jvm 1    | 2026/08/26 09:57:00 | W [g.LicenseManager              ] [09:57:00.120]: Could not read license from HASP key. HASP login() failed. Last error = 14.
INFO   | jvm 1    | 2026/08/26 10:05:11 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:11.015]: Java version: 17.0.19
INFO   | jvm 1    | 2026/08/26 10:05:11 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:11.015]: Eclipse Milo OPC UA Stack version: 1.1.4
INFO   | jvm 1    | 2026/08/26 10:05:11 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:11.015]: Eclipse Milo OPC UA Server SDK version: 1.1.4
INFO   | jvm 1    | 2026/08/26 10:05:12 | I [t.h.gw_module_bridge          ] [10:05:12.354]: Historian Core module bridge successfully registered.
INFO   | jvm 1    | 2026/08/26 10:05:16 | I [c.i.s.g.SqlHistorianLicense   ] [10:05:16.720]: SQL Historian access level changed: Demo_Enabled -> Full
INFO   | jvm 1    | 2026/08/26 10:05:16 | I [G.L.A.AlarmNotificationService] [10:05:16.770]: Remote Alarm Notification Manager initialized successfully.
INFO   | jvm 1    | 2026/08/26 10:05:18 | I [IgnitionGateway               ] [10:05:18.795]: Skipping VACUUM due to ignition.skipConfigDbVacuum=true.
INFO   | jvm 1    | 2026/08/26 10:05:19 | I [g.SecretProviderManager       ] [10:05:19.273]: Startup completed in 2 ms
INFO   | jvm 1    | 2026/08/26 10:05:19 | I [g.OAuth2ClientManager         ] [10:05:19.274]: Startup complete in 0 ms
INFO   | jvm 1    | 2026/08/26 10:05:19 | I [g.EmailProfileManager         ] [10:05:19.274]: Startup complete in 0 ms
INFO   | jvm 1    | 2026/08/26 10:05:19 | I [g.SecurityLevelManager        ] [10:05:19.281]: Startup completed in 5 ms
INFO   | jvm 1    | 2026/08/26 10:05:19 | I [g.IdentityProviderManager     ] [10:05:19.307]: Startup completed in 25 ms
INFO   | jvm 1    | 2026/08/26 10:05:19 | I [g.OIDCProviderManager         ] [10:05:19.797]: Started up complete in 489 ms
INFO   | jvm 1    | 2026/08/26 10:05:20 | I [t.m.provider                  ] [10:05:20.108]: Tag provider 'System' is initialized. Starting to load tags... provider=System
INFO   | jvm 1    | 2026/08/26 10:05:20 | I [P.InternalDatabase            ] [10:05:20.131]: internal database "references.idb" started up successfully. provider=System
INFO   | jvm 1    | 2026/08/26 10:05:20 | I [c.i.i.g.t.r.DbTagReferenceStore] [10:05:20.132]: Tag Trace store started. provider=System
INFO   | jvm 1    | 2026/08/26 10:05:20 | I [t.m.provider                  ] [10:05:20.226]: Tag provider `System` completed tag loading in 78 ms
INFO   | jvm 1    | 2026/08/26 10:05:20 | I [c.i.i.g.t.r.StatefulTagReferenceStore] [10:05:20.292]: Creating and enabling new tag reference store for provider: xxxxx
INFO   | jvm 1    | 2026/08/26 10:05:20 | I [t.m.provider                  ] [10:05:20.298]: Tag provider 'xxxxx' is initialized. Starting to load tags... provider=xxxxx
INFO   | jvm 1    | 2026/08/26 10:05:20 | I [P.InternalDatabase            ] [10:05:20.304]: internal database "references.idb" started up successfully. provider=xxxxx
INFO   | jvm 1    | 2026/08/26 10:05:20 | I [c.i.i.g.t.r.DbTagReferenceStore] [10:05:20.305]: Tag Trace store started. provider=xxxxx
INFO   | jvm 1    | 2026/08/26 10:05:23 | E [t.e.expressionParser          ] [10:05:23.553]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:23 | E [t.e.expressionParser          ] [10:05:23.802]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:23 | E [t.e.expressionParser          ] [10:05:23.964]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:24 | E [t.e.expressionParser          ] [10:05:24.504]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:24 | E [t.e.expressionParser          ] [10:05:24.723]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:25 | E [t.e.expressionParser          ] [10:05:25.045]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:25 | E [t.e.expressionParser          ] [10:05:25.123]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:25 | E [t.e.expressionParser          ] [10:05:25.938]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:27 | E [t.e.expressionParser          ] [10:05:27.177]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:27 | E [t.e.expressionParser          ] [10:05:27.817]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:28 | E [t.e.expressionParser          ] [10:05:28.700]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:29 | E [t.e.expressionParser          ] [10:05:29.390]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:31 | E [t.e.expressionParser          ] [10:05:31.049]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:31 | E [t.e.expressionParser          ] [10:05:31.167]: Invalid reference xxxxxx   in expression tag tag=xxxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:36 | I [t.m.provider                  ] [10:05:36.026]: Tag provider `xxxxx` completed tag loading in 15 seconds
INFO   | jvm 1    | 2026/08/26 10:05:36 | I [c.i.i.g.t.r.StatefulTagReferenceStore] [10:05:36.031]: Creating and enabling new tag reference store for provider: xxxxx
INFO   | jvm 1    | 2026/08/26 10:05:36 | I [t.m.provider                  ] [10:05:36.032]: Tag provider 'xxxxx' is initialized. Starting to load tags... provider=xxxxx
INFO   | jvm 1    | 2026/08/26 10:05:36 | I [P.InternalDatabase            ] [10:05:36.037]: internal database "references.idb" started up successfully. provider=xxxxx
INFO   | jvm 1    | 2026/08/26 10:05:36 | I [c.i.i.g.t.r.DbTagReferenceStore] [10:05:36.038]: Tag Trace store started. provider=xxxxx
INFO   | jvm 1    | 2026/08/26 10:05:47 | I [t.m.provider                  ] [10:05:47.451]: Tag provider `xxxxx` completed tag loading in 11 seconds
INFO   | jvm 1    | 2026/08/26 10:05:47 | I [c.i.i.g.t.r.StatefulTagReferenceStore] [10:05:47.480]: Creating and enabling new tag reference store for provider: Project
INFO   | jvm 1    | 2026/08/26 10:05:47 | I [t.m.provider                  ] [10:05:47.480]: Tag provider 'Project' is initialized. Starting to load tags... provider=Project
INFO   | jvm 1    | 2026/08/26 10:05:47 | I [P.InternalDatabase            ] [10:05:47.486]: internal database "references.idb" started up successfully. provider=Project
INFO   | jvm 1    | 2026/08/26 10:05:47 | I [c.i.i.g.t.r.DbTagReferenceStore] [10:05:47.487]: Tag Trace store started. provider=Project
INFO   | jvm 1    | 2026/08/26 10:05:48 | W [t.e.a.history                 ] [10:05:48.216]: xxxxxx History is enabled, but history provider is not defined. tag=direct
INFO   | jvm 1    | 2026/08/26 10:05:48 | W [t.e.a.h.container             ] [10:05:48.220]: Created an errored historian container for Multikey[[Project, , OnChange]]: Error_Configuration("History provider not defined") tag=direct
INFO   | jvm 1    | 2026/08/26 10:05:48 | E [t.e.expressionParser          ] [10:05:48.291]: Invalid reference xxxxxxxx in expression tag xxxxxxxxx tag=_NextOnDispTag
INFO   | jvm 1    | 2026/08/26 10:05:48 | E [t.e.expressionParser          ] [10:05:48.292]: Invalid reference xxxxxxxx in expression tag xxxxxxxxx tag=_NextOnDispTag
INFO   | jvm 1    | 2026/08/26 10:05:48 | I [t.e.dispatcher                ] [10:05:48.313]: ProjectManager not yet running, rescheduling for +2 seconds tag=_manualTrigger
INFO   | jvm 1    | 2026/08/26 10:05:48 | E [t.e.expressionParser          ] [10:05:48.386]: Invalid reference xxxxxxxx in expression tag xxxxxx tag=xxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:48 | E [t.e.expressionParser          ] [10:05:48.728]: Invalid reference xxxxxxxx in expression tag xxxxxx tag=xxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:48 | E [t.e.expressionParser          ] [10:05:48.743]: Invalid reference xxxxxxxx in expression tag xxxxxx tag=xxxxxxx
INFO   | jvm 1    | 2026/08/26 10:05:53 | I [t.m.provider                  ] [10:05:53.555]: Tag provider `Project` completed tag loading in 6 seconds
INFO   | jvm 1    | 2026/08/26 10:05:53 | I [i.UserSourceManager           ] [10:05:53.597]: Starting up...
INFO   | jvm 1    | 2026/08/26 10:05:53 | I [AuditManager                  ] [10:05:53.657]: AuditManager starting up...
INFO   | jvm 1    | 2026/08/26 10:05:53 | I [ImageManager                  ] [10:05:53.854]: Starting up...
INFO   | jvm 1    | 2026/08/26 10:05:53 | I [Project                       ] [10:05:53.874]: Starting project: ProjectName-Main project=ProjectName-Main
INFO   | jvm 1    | 2026/08/26 10:05:54 | I [DesignerAuthTokenRecords      ] [10:05:54.407]: Starting up...
INFO   | jvm 1    | 2026/08/26 10:05:54 | I [DesignerAuthTokenRecords      ] [10:05:54.419]: Startup completed in 11 ms
INFO   | jvm 1    | 2026/08/26 10:05:54 | I [SessionManager                ] [10:05:54.422]: Starting up...
INFO   | jvm 1    | 2026/08/26 10:05:54 | I [c.i.i.g.ScheduledBackupManager] [10:05:54.436]: Registered scheduled backups for cron schedule: 30 * * * *
INFO   | jvm 1    | 2026/08/26 10:05:54 | I [AutomaticThreadDumpManager    ] [10:05:54.437]: Starting up...
INFO   | jvm 1    | 2026/08/26 10:05:54 | I [c.i.i.g.m.MulticastScheduler  ] [10:05:54.443]: Registered MulticastScheduler on multicast address: 231.1.1.1 using send port 4445 and receive port 4446
INFO   | jvm 1    | 2026/08/26 10:05:54 | I [g.ClientFallbackController    ] [10:05:54.444]: Fallback Socket Controller starting.
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [IgnitionGateway               ] [10:05:56.087]: Platform module services initialized.
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [G.Manager                     ] [10:05:56.106]: WSChannel manager started.
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [m.M.Routing                   ] [10:05:56.107]: Setting max proxy route depth = 0
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [g.g.WSChannelManager          ] [10:05:56.186]: Gateway network channel manager started successfully. Protobuf gzip compression threshold set to 1000 bytes
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [g.ModuleManager               ] [10:05:56.196]: Starting up modules
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [ModuleInstance                ] [10:05:56.197]: Starting up module 'com.inductiveautomation.symbol-factory' v8.3.8 (b2026071409)... module-name=Symbol Factory
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [ModuleInstance                ] [10:05:56.197]: Starting up module 'com.inductiveautomation.opcua' v10.3.8 (b2026071409)... module-name=OPC-UA
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:56.883]: Binding endpoint opc.tcp://computername:62541 to localhost:62541 [Basic256Sha256/SignAndEncrypt] module-name=OPC-UA
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:56.937]: Binding endpoint opc.tcp://computername:62541/discovery to localhost:62541 [None/None] module-name=OPC-UA
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:56.938]: Binding endpoint opc.tcp://localhost:62541 to localhost:62541 [Basic256Sha256/SignAndEncrypt] module-name=OPC-UA
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:56.938]: Binding endpoint opc.tcp://localhost:62541/discovery to localhost:62541 [None/None] module-name=OPC-UA
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:56.938]: Binding endpoint opc.tcp://127.0.0.1:62541 to localhost:62541 [Basic256Sha256/SignAndEncrypt] module-name=OPC-UA
INFO   | jvm 1    | 2026/08/26 10:05:56 | I [o.e.m.o.s.s.OpcUaServer       ] [10:05:56.938]: Binding endpoint opc.tcp://127.0.0.1:62541/discovery to localhost:62541 [None/None] module-name=OPC-UA
INFO   | jvm 1    | 2026/08/26 10:05:57 | I [OpcUaModule                   ] [10:05:57.004]: Routes mounted module-name=OPC-UA
INFO   | jvm 1    | 2026/08/26 10:05:57 | I [ModuleInstance                ] [10:05:57.004]: Starting up module 'com.inductiveautomation.historian' v1.3.8 (b2026071409)... module-name=Historian Core
INFO   | jvm 1    | 2026/08/26 10:05:57 | I [h.manager                     ] [10:05:57.004]: Starting... module-name=Historian Core
INFO   | jvm 1    | 2026/08/26 10:05:57 | Reading log configuration from C:\Program Files\Inductive Automation\Ignition\data\var\com.inductiveautomation.historian\corehistorian\conf\log.conf
INFO   | jvm 1    | 2026/08/26 10:05:57 | I [o.e.m.o.s.c.OpcUaClient       ] [10:05:57.383]: Java version: 17.0.19
INFO   | jvm 1    | 2026/08/26 10:05:57 | I [o.e.m.o.s.c.OpcUaClient       ] [10:05:57.383]: Eclipse Milo OPC UA Stack version: 1.1.4
INFO   | jvm 1    | 2026/08/26 10:05:57 | I [o.e.m.o.s.c.OpcUaClient       ] [10:05:57.383]: Eclipse Milo OPC UA Client SDK version: 1.1.4
INFO   | jvm 1    | 2026/08/26 10:05:58 | W [o.e.m.o.s.c.s.DefaultClientCertificateValidator] [10:05:58.475]: check suppressed: certificate failed hostname check: C=US,ST=CA,L=Folsom,O=Inductive Automation,CN=Ignition OPC UA Server
INFO   | jvm 1    | 2026/08/26 10:19:15 | I [h.p.CoreHistorian             ] [10:19:15.751]: Historian 'HISTORIAN' started module-name=Historian Core, historian-name=HISTORIAN
INFO   | jvm 1    | 2026/08/26 10:19:15 | I [h.ModuleHook                  ] [10:19:15.929]: Historian module started. module-name=Historian Core
INFO   | jvm 1    | 2026/08/26 10:19:15 | I [ModuleInstance                ] [10:19:15.931]: Starting up module 'com.inductiveautomation.eventstream' v1.3.8 (b2026071409)... module-name=Event Streams
INFO   | jvm 1    | 2026/08/26 10:19:15 | I [c.i.e.g.GatewayEventStreamManager] [10:19:15.931]: Started module-name=Event Streams
INFO   | jvm 1    | 2026/08/26 10:19:15 | I [ModuleInstance                ] [10:19:15.940]: Starting up module 'com.inductiveautomation.jdbc.postgresql' v1.3.8 (b2026071409)... module-name=PostgreSQL JDBC Driver
INFO   | jvm 1    | 2026/08/26 10:19:15 | I [ModuleInstance                ] [10:19:15.940]: Starting up module 'com.inductiveautomation.perspective' v3.3.8 (b2026071409)... module-name=Perspective
INFO   | jvm 1    | 2026/08/26 10:19:17 | W [h.s.s.debouncer               ] [10:19:17.441]: Failed to store 4,383 points for type: GENERIC historian-name=HISTORIAN
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [PerspectiveAuthTokenRecords   ] [10:19:18.111]: Starting up... module-name=Perspective
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [PerspectiveAuthTokenRecords   ] [10:19:18.112]: Startup completed in 0 ms module-name=Perspective
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [ModuleInstance                ] [10:19:18.166]: Starting up module 'com.inductiveautomation.opcua.drivers.logix' v6.3.8 (b2026071409)... module-name=Logix Driver
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [ModuleInstance                ] [10:19:18.167]: Starting up module 'com.inductiveautomation.opcua.drivers.bacnet' v3.3.8 (b2026071409)... module-name=BACnet Driver
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [ModuleInstance                ] [10:19:18.171]: Starting up module 'com.inductiveautomation.opcua.drivers.modbus' v8.3.8 (b2026071409)... module-name=Modbus Driver
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [ModuleInstance                ] [10:19:18.173]: Starting up module 'com.inductiveautomation.historian.sql' v1.3.8 (b2026071409)... module-name=SQL Historian
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [ModuleInstance                ] [10:19:18.173]: Starting up module 'com.inductiveautomation.alarm-notification' v7.3.8 (b2026071409)... module-name=Alarm Notification
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [ModuleInstance                ] [10:19:18.193]: Starting up module 'com.inductiveautomation.webdev' v6.3.8 (b2026071409)... module-name=WebDev
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [ModuleInstance                ] [10:19:18.194]: Starting up module 'com.inductiveautomation.reporting' v7.3.8 (b2026071409)... module-name=Reporting
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [IgnitionGateway               ] [10:19:18.228]: Ignition[state=STARTING] ContextState = RUNNING
INFO   | jvm 1    | 2026/08/26 10:19:18 | I [IgnitionGateway               ] [10:19:18.228]: Gateway started in 1353 seconds.
Looks like it's the core historian that's taking a long time to start up :person_shrugging: I don't have any experience with it though
It probably doesn't help running the emulators on the same PC as you Ignition server.
Virtually all of that 22-minute startup time is getting swallowed by just two specific spots:
  • The HASP Licensing Timeout (~8 minutes?): Right near the start, the JVM gets stuck trying to read a physical HASP license key (HASP login() failed. Error 14). If you aren't using a physical USB dongle, it just sits there waiting for a hardware response before finally timing out and moving on. Maybe issue is driver passthrough with the VM.
  • The Historian Core Hang (~13 minutes?): The big offender. The gateway freezes up completely while trying to start the Historian Core module right after an OPC UA certificate warning. The moment it finally unfreezes, it immediately logs an error for dropping over 4,000 data points.
There's also about half a minute of extra noise from broken tag expression references (Invalid reference xxxxxx) cluttering up the load sequence.
Honestly, if a gateway takes long enough to boot that you can go brew a pot of coffee, eat breakfast, and come back—only for its very first act upon waking to be dropping 4,000 historian points—I can only imagine what kind of chaos is going on behind the scenes during live operations. If runtime feels like driving with the parking brake on, these logs make a lot of sense.
You may want to give a try to the Gateway Analyzer module. It will help track down thread locks, resource bottlenecks, and hidden performance drains so you aren't left guessing.
The best way to troubleshoot this is using jstack to get thread dumps at the couple spots in the logs it seems to be stalled. Support can help you out with that.
I know we have some kind of relationship with you guys, but this post is gross. You can do better.
jstackis actually the route I went. I think the fix was networking - the connections were crazy... IPV6 on where it wasn't supposed to be, DNS server was incorrect (unreachable), and nslookup was failing on the computer name but not ping. This has all been corrected.
I also reset the Core historian module by disabling it and having it recreate the database - which wasn't an issue because this wasn't a production environment.
Thanks for the help.
Shea