I’ve left it running for minutes with no change on Ignition 8.1.18 and several earlier versions. I don’t recall for certain if this ever worked or not, but thought it had back in Ignition 7.9.something. We’d like to see the same stats on here as for the Logix driver to see how the ControlLogix bridge-DH+ network and SLC 5/04 are handling the tag requests we’re making. Should this be working, or are no stats expected for DHRIO connections?
Does the driver periodically browse the processor if we don’t select the Disable Processor Browse option, or is it only relevant to browsing from Designer?
Thanks for confirming, @pturmel. What loggers might be relevant to adjust logging level? I don’t see anything that looks relevant in the logs on gateway web page. There’s nothing logging at the time we attempt to load details page at default info logging levels and the OPC UA, driver adapter, and gateway loggers I set to trace didn’t turn anything up at the time of access either (they are logging lists of reads and occasional writes from operators).
Josh Hansen in support figured it out. Don’t use special characters in device name. In our case, this device had an ampersand and slash in it. A new connection without those in it worked great. A new connection with an ampersand and slash in name also exhibited forever loading.